suction line size for 5 ton unit

I have a 5 ton unit (goodman unit) liquid line 3/8 and suction line 1 1/8 and the run is about 45ft long. I was told that i would have a lot of problem. does any know what kind of problem would i be facing? last summer the unit run all summer long and one problem arise (one of the wire connect to the contactor relay on the out side unit was burn up at the ternimal end).
 
Sponsored Links
  #2  
Old 01-26-03, 10:18 AM
hvac4u's Avatar
Member
Join Date: Aug 2001
Location: NW atlanta
Posts: 3,147
Received 0 Votes on 0 Posts
i believe

goodman rates the suction line at 45 ft to be 7/8. if it did not give you trouble why change it? 1 1/8 is ok from what i can tell. is the condenser above, below or level with the evap coil? to get technical, lift would have to be considered.
 
  #3  
Old 01-26-03, 01:08 PM
bigjohn
Visiting Guest
Posts: n/a
Refrigerant tubing is sized by OD- Outside Diameter. Refrigerant tubing is sized based on equivalent length. The idea is that whatever state the refrigerant is flowing in, it will see the fittings/valves as though each one were X number of feet. So, if you have 45 feet of tubing, you then count the number and type fittings/valves and calculate the equivalent length. Your 45 foot run is probably closer to 50 to 60 feet of equivalent length. 1-1/8"OD is fine on the suction line, especially if the condensing unit is below the cooling coil. The 3/8" OD liquid line might be a problem. My charts call for 1/2"OD. If your condensing unit is below the evaporator, then you're probably ok. I agree with hvac4u, you made it thru at least 1 season, you're probably going to be ok. One thing that is important is that, on horizontal vapor lines, you want to pitch the line in the direction of flow at 1/4" per 10 feet of horizontal run.
 
  #4  
Old 01-26-03, 02:09 PM
jova757
Visiting Guest
Posts: n/a
my coil is about 8 feet above the condensor unit.
thank you for the very good info. this is the best site i have been visited. every information is alway good.
 
  #5  
Old 01-26-03, 02:21 PM
GregH's Avatar
Super Moderator
Join Date: Jan 2001
Location: Manitoba
Posts: 9,988
Received 8 Votes on 8 Posts
jova757:

My charts show your capacity and line length to be right in the middle of 7/8" and 1 1/8".
Your installer made the correct line size choice for the higher evaperator.

If the coil were 8' below the evaperator I would have gone with 7/8"
 
  #6  
Old 01-27-03, 08:41 AM
jova757
Visiting Guest
Posts: n/a
unit size

how do i find out what size is my condensor and my evap. coil? what do you look for to get this info? if the tech-man said your unit is a 5 ton would you take his word for it or there is a way to find out?
 
  #7  
Old 01-27-03, 12:09 PM
GregH's Avatar
Super Moderator
Join Date: Jan 2001
Location: Manitoba
Posts: 9,988
Received 8 Votes on 8 Posts
Exclamation

jova757:

I have merged your latest new thread with an older post.
I have also found two other threads on this same subject.

Please use the reply button to ask questions relating to the same piece of equipment.

Thanks.

The model number found on the evaperator coil and outdoor unit can be used to determine it's capacity.

Post those numbers here.
 
  #8  
Old 01-29-03, 10:40 AM
jova757
Visiting Guest
Posts: n/a
heat pump making noise

house two level in tx
heat pump 5 ton 12 seer 3/8 for small line 3/4 for big line
out door unit to indoor unit is about 45ft with arise of 18ft high
out side temp is about 50deg f
with a scroll compressor control by a digital honeywell thermostat
about one yr old making all kind of noise from a buzz sound to a loud bann
 
  #9  
Old 01-29-03, 12:50 PM
bigjohn
Visiting Guest
Posts: n/a
Where's the noise? In the outdoor section or the indoor section? If it's outdoors first lalce to look is the compressor contactor. It may be malfunctioning or full of ants/critters.
 
  #10  
Old 01-29-03, 06:47 PM
jova757
Visiting Guest
Posts: n/a
the out door unit all the electrical is clean
 
  #11  
Old 01-31-03, 09:04 PM
jova757
Visiting Guest
Posts: n/a
ask the expert

what does filter\drier do for a/c unit?

I 've read a statement on a/c that "the a/c unit is operate correctly if the temp. on the return side and the temp. on the supply side is 20 degree difference" is this truth or not? if it is the truth is it the same thing with heating?

what cause an a/c unit to have the use of start capacitor?
 
  #12  
Old 02-01-03, 06:54 AM
hvac4u's Avatar
Member
Join Date: Aug 2001
Location: NW atlanta
Posts: 3,147
Received 0 Votes on 0 Posts
just the facts

capacitors are used to give added torque to the start winding in a single phase compressor or fan. a drier removes moisture and contaminants from the refrigerant system using dessicants. the 20 degree drop you describe is excellent for temp difference between return and supply air.
 
  #13  
Old 02-02-03, 06:14 PM
jova757
Visiting Guest
Posts: n/a
over and under

what would happen if you over charge the a/c unit and if you under charge the unit?
 
  #14  
Old 02-02-03, 08:46 PM
GregH's Avatar
Super Moderator
Join Date: Jan 2001
Location: Manitoba
Posts: 9,988
Received 8 Votes on 8 Posts
Question I have merged four threads to try to figure out the root of your problem.

jova757:

I'm really puzzled.

I have asked you to post questions on the same equipment in the same thread so that we can make some sense of your issues.

I have now joined two more threads to make one so that we can get an idea about what's going on with your equipment.

1. We are still waiting to hear about the coil and unit model numbers so we can determine if you have the correct line size.
2. We are still trying to determine why your unit is noisy.
3. Hopefully we have answered your capacitor question.
4. We now have a new question on refrigerant charging.

At first you told us you have 1 1/8 suction line and now it is 7/8.

What do you really need to know???
 
  #15  
Old 02-03-03, 07:53 AM
jova757
Visiting Guest
Posts: n/a
yes i have 1 1/8 line and i ask you what would happen if the line were let said 3/4 line? I think you come up with that 7/8line. sorry for the miss understanding
 
  #16  
Old 02-03-03, 12:02 PM
GregH's Avatar
Super Moderator
Join Date: Jan 2001
Location: Manitoba
Posts: 9,988
Received 8 Votes on 8 Posts
jova757:

You are right, you said 3/4 inch and not 7/8.

jova757 wrote:

"I have a 5 ton unit (goodman unit) liquid line 3/8 and suction line 1 1/8....."

"heat pump 5 ton 12 seer 3/8 for small line 3/4 for big line "

It would be helpful if you would ask a question relating to a specific problem you may have.
It is ok to ask technical questions, but you have not responded to our request for specific information to help complete answers to questions you have already asked.

I'll take a wild guess in that you say your system is about a year old.
Now that the warranty may have just, or is about to expire, do you have some concerns that there may be something wrong with your system?

Like I said, ask away, we just not may be getting to the root of your problem.

And again, please use the reply button to ask any more questions.
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
Display Modes
 
Ask a Question
Question Title:
Description:
Your question will be posted in: