I have a Carrier 4.5 ton AC unit that has recenlty continued to cycle wether I have the thermostat in Heat or Cool. Even after the blower shuts down the outside unit continues to run and cycle. In heat it runs - goes into defrost mode- and then runs again. In cool it continues to run until the lagre line starts to freeze. What should I look to replace? Control board, a relay, coil?

Thanks
 
Sponsored Links
  #2  
Old 04-02-03, 08:42 PM
mattison's Avatar
Member
Join Date: Mar 2003
Location: Cinti, OH
Posts: 5,549
Received 0 Votes on 0 Posts
You should really call a pro.

If you know what the contactor in the outdoor unit looks like check it with the power off and see if it's stuck. If so replace it.
 
  #3  
Old 04-02-03, 09:55 PM
Member
Join Date: Nov 2002
Location: Massachusetts
Posts: 1,819
Received 0 Votes on 0 Posts
Cool Elimination....

Try to eliminate the control in this case the thermostat...Did you by chance replace this recently?? You'll need 3 jumpers.. Kill the power first...Label and then remove the thermostat wires at the air handler terminal board. First place a jumper from R to Y and R to G... Apply power...the unit should run in the heat mode...now place the 3rd jumper from the O terminal to R and the reversing valve should pop over to run in cooling. Be carefull not to touch the jumper to ground or you could blow the transformer. This is all low voltage (24V)...now remove the connections from R and everything should stop..Start there..If all this works OK , you'll probably be replacing the T'stat...or the stat wire......
 
  #4  
Old 04-03-03, 12:38 PM
Ed Imeduc's Avatar
Member
Join Date: Aug 2002
Location: Mountain Williams Missouri
Posts: 18,389
Received 0 Votes on 0 Posts
A/C runs

You said . In cool it runs till the large line starts to frost. This sounds like your are also low on freon and the unit shuts off on the low pressure switch. You should get a tech to look at it and see if it is the wire, tstat, or relay. ED
 
  #5  
Old 04-03-03, 05:28 PM
khussey
Visiting Guest
Posts: n/a
It's Fixed !!!

Thanks all for the help folks. I was able to isolate it to the contactor.

The points on 1 leg were pitted closed. We are running fine.
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
Display Modes
 
Ask a Question
Question Title:
Description:
Your question will be posted in: