Furnace sizing for new construction

Reply

  #1  
Old 05-08-03, 07:29 AM
noake
Visiting Guest
Posts: n/a
Furnace sizing for new construction

Hello,
I just purchased a new house that is 2100 sf, with another 1000 sf of basement that can be finished. I had my good friend, who is an AC contractor out to install an AC unit to the furnace that came with the house. THe existing new furnace (which I have not even turned on) is 70,000 BTU at 80%, so 56,000 effective. The house is 2 stories, and then the basement. He says that the furnace is way undersized for the house and it will be hard to install the proper size AC unit, becuase of plenum dimensions being too small for 3 tons of cooling. He says that someone probably made amistake, and that they usually install 70k units in 1000-1500 sf homes. The contractor and builder who built the development said that they put the same size in all homes, and they have had no complaints. There is no doubt in my mind that they probably skimped. But, my question is- do you think they will do anything for me? My friend says he can get a 100,000 btu unti for $500 and put it in with the AC and probably save me some headache down the road. Do you think the builder or contractor would take back the existing 70,000 btu unit? What if I left it in, what would be the potential problems down teh road for me? Any advice would be greatly appreciated. Also- does anyone know of a chart that is used to figure furnace sizing based on square footage of home? Or a website?
 
Sponsored Links
  #2  
Old 05-08-03, 02:55 PM
KField's Avatar
Member
Join Date: Dec 2002
Location: Easton, PA
Posts: 3,245
Received 0 Votes on 0 Posts
Do a heat gain if you haven't already. 3 tons sounds like alot of cooling for a house your size. Do you have a lot of glass? What part of the country are you in? I wouldn't tear out a brand new furnace unless you have found that it won't carry the load. It is usually surprising how the fudge factors lead people to oversize equipment.

Ken
 
  #3  
Old 05-08-03, 03:51 PM
GregH's Avatar
Super Moderator
Join Date: Jan 2001
Location: Manitoba
Posts: 10,135
Received 35 Votes on 33 Posts
noake:

There is no such thing as sizing by square footage and what people "usually" install doesn't cut it either.

A heat load calculation must be done to be sure. If the builder installs 70k furnaces they could work ok.

The way to do it is calculate the heat/cool load and then select the ductwork for the capacity you need.

Some have purchased a single use calc here and were happy but I havn't heard how the free download works:http://www.hvaccomputer.com/main.asp

Considering how long you will have to live with this it would be worth the fifty bucks to get the full version.
 
Reply
Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
 
Ask a Question
Question Title:
Description:
Your question will be posted in: