Hi,

I am looking to install a swamp cooler in my house. There has never been one before.

I have two q's related to this:

1) How to determine the CFM of the unit. I have seen a formula (ft^3/2 = CFM), is this correct? Seems a little high since it computes a much higher CFM than is easily available (building centers...).

2) How to tie into duct work. What seems most logical to me is to tie into my existing furnace's cold air return. Is this OK, or are there reasons not to do so. If it's OK, do I then block the cold air return trunk from the house and only feed it swamp cooler air, or do I leave the "regular" CAR open and let both air streams mix?

I would like to tie into the duct system since (by my thinking) each room would get some cooling; I wouldn't need to leave bedroom/bathroom/[any room I don't want the dog to have access to] doors open.

FYI, I live N. CO, lately temps are around 100F with an RH ~40-50 at midnight, dropping to ~10 by noon and staying low for the majority of the day.
 
Sponsored Links
  #2  
Old 07-14-03, 02:55 PM
Ed Imeduc's Avatar
Member
Join Date: Aug 2002
Location: Mountain Williams Missouri
Posts: 18,389
Received 0 Votes on 0 Posts
evaporative cooling

All the units have the cfm on them a small 1/3 hp about 2000 cfm On up to the big ones at 5600 cfm on a 1 hp.. I have never heard of any one trying to put it in the duct work in a home on the furnace,I know I dont and have put a lot in. Think about it you want to put air in the home ,it has to get out some where. So if its blowing in and you open a window in a room down the hall the air will go down there to get out. So if you open all the windows a little all the room will get the air. If you blow this wet air in your duct work for the furnace you will have a mess. ED
 
  #3  
Old 07-15-03, 09:03 AM
Member
Thread Starter
Join Date: Feb 2003
Location: Fort Collins, CO, USA
Posts: 9
Received 0 Votes on 0 Posts
Thanks for the reply Ed.

I guess I wasn't clear on the first question though. What I meant was, How do you compute the needed CFM?

IE) An 1800 ft^2 house needs a cooler that moves _____ CFM.

Thanks
 
  #4  
Old 07-15-03, 10:21 AM
Ed Imeduc's Avatar
Member
Join Date: Aug 2002
Location: Mountain Williams Missouri
Posts: 18,389
Received 0 Votes on 0 Posts
cooler

The good book said for where you are

Cubic ft of home---divide by min. per air change, where you are at it's 3 so I get at 0"static pressure 4800 cfm for the home. Or a unit with about a 3/4 hp on it. That would give you a 5000 cfm.
This is out of Grainger. ED
 
  #5  
Old 07-15-03, 02:05 PM
Member
Thread Starter
Join Date: Feb 2003
Location: Fort Collins, CO, USA
Posts: 9
Received 0 Votes on 0 Posts
Thanks for the info Ed!
 
  #6  
Old 07-15-03, 02:17 PM
Ed Imeduc's Avatar
Member
Join Date: Aug 2002
Location: Mountain Williams Missouri
Posts: 18,389
Received 0 Votes on 0 Posts
cool

With this you put it so it will blow out like in the center of the home. Then you open the windows in the rooms you want to cool and let the air go out that way dont put this into the furnace duct work. ED
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
 
Ask a Question
Question Title:
Description:
Your question will be posted in: