Hello all...

My electric furnace keeps tripping its circut breaker. It is on a 30 amp breaker but in heat is pulling 45 amps. After 5 minutes, the breaker trips (of course). In A/C mode, the furnace is only pulling 1 amp. When the heat is on, all seems to be working normally except for the current at the breaker.

Where should I start trouble shooting? Any obvious components to check?

Thanks for the help!

Michael
 
  #2  
Old 12-26-03, 11:00 AM
Ed Imeduc's Avatar
Member
Join Date: Aug 2002
Location: Mountain Williams Missouri
Posts: 18,386
Received 1 Vote on 1 Post
Lightbulb FURNACE

If the unit calls for a 45 amp breaker you have to put a 45 amp beaker on it right now. Look at the wire lay out there on the door it should saywhat you should have there. When the AC is on what you will read on amps is for just the blower in the blower unit .Should be a little more amps per leg cause its wired 220V on the blower. ED
 
  #3  
Old 12-26-03, 11:55 AM
T
Member
Join Date: Jan 2002
Location: Chicago
Posts: 1,915
Received 0 Votes on 0 Posts
How did you measure 45A?
Is this a new installation? As Ed said, 1A is too low.

Don't forget, if you change the breaker to a larger size you also need to change (or at least make sure) that the wiring is also capable of handling 45A (you'll probably need a #6 wire).
 
 