My girlfriend's fan limit control was not allowing for the blower to shut off after the furnace stopped running. I moved the three around a little bit and it seems to be working all right again. First, I am wondering what the three different settings should be for on the fan limit control Dial: The current settings are OFF-ON- Now at 100; ON - 150; OFF- 200--- I also watched the fan limit control as the furnace cooled down and it made a squeeky noise as it slid to the next position. Will this eventually need to be replaced due to it sticking? Not sure
 
  #2  
Old 11-01-04, 01:48 PM
Ed Imeduc's Avatar
Member
Join Date: Aug 2002
Location: Mountain Williams Missouri
Posts: 18,386
Received 1 Vote on 1 Post
Wink

Dont know for sure what you have there. INFO help's that 200o should be the limit control. most fans are set for fan on 110-115on and fan off 95 to a 100. Is the filter clean and the control element clean??