Loud Furnace


  #1  
Old 01-27-05, 02:49 PM
RaiderZJ
Visiting Guest
Posts: n/a
Loud Furnace

I have a gas forced air furnace. It has one intake vent in the first floor hallway, which is in the center of the house. Here is my question; when the blower turns on, its pretty loud. Not a grumbling or bad type of noise, it seems like its an air flow type noise. Is there any way to quiet it down? Thanks
 
  #2  
Old 01-27-05, 04:25 PM
Jay11J's Avatar
Member
Join Date: Sep 2001
Location: Rochester, Minnesota
Posts: 16,984
Upvotes: 0
Received 0 Upvotes on 0 Posts
How big is this return? The return vent itself or the duct work maybe too small for your sytem?

This return in the ceiling or on the floor?
 
  #3  
Old 01-27-05, 05:30 PM
mattison's Avatar
Member
Join Date: Mar 2003
Location: Cinti, OH
Posts: 5,315
Upvotes: 0
Received 0 Upvotes on 0 Posts
Also is it a new noise or has it alway been there?
 
  #4  
Old 01-27-05, 05:33 PM
Ed Imeduc's Avatar
Member
Join Date: Aug 2002
Location: Mountain Williams Missouri
Posts: 17,505
Upvotes: 0
Received 1 Upvote on 1 Post
Wink

If its just the air noise . lots of time we take and line the inside of the blower part with scrap fiberglass duct board works real good. also put your hand on the grill if the noise stops the grill resonates so you have to bend the bars just a little and it can stop.


ED
 
  #5  
Old 01-28-05, 02:54 PM
RaiderZJ
Visiting Guest
Posts: n/a
Thanks for the replies. The return vent is 14 x 20. The vent is also a straight shot to the blower (14" from the wall to the furnace) Any tips on eliminating the noise? Thanks
 
  #6  
Old 01-28-05, 03:41 PM
Jay11J's Avatar
Member
Join Date: Sep 2001
Location: Rochester, Minnesota
Posts: 16,984
Upvotes: 0
Received 0 Upvotes on 0 Posts
That vent sounds pretty small..So, with that small of a return vent, you will get the loud air rush sound. How many BTU is the furnace?
 
  #7  
Old 01-28-05, 03:58 PM
Ed Imeduc's Avatar
Member
Join Date: Aug 2002
Location: Mountain Williams Missouri
Posts: 17,505
Upvotes: 0
Received 1 Upvote on 1 Post
Wink

Out of the box here but that 14X20 coldair sounds good say for 3 ton on so. But what is the filter grill on it ???? Should be about a 20X20 or bigger ,Id say

ED
 
  #8  
Old 01-28-05, 04:39 PM
RaiderZJ
Visiting Guest
Posts: n/a
The vent grill is 22 x 18. But the duct going to the furnace is only the 14 x 20. So the grill is covering a lot of wall. Should I somehow enlarge the return duct to accomadate the full size of the grill?

The manual says it is a 75k BTU input/60k BTU output.
 
  #9  
Old 01-28-05, 05:14 PM
Ed Imeduc's Avatar
Member
Join Date: Aug 2002
Location: Mountain Williams Missouri
Posts: 17,505
Upvotes: 0
Received 1 Upvote on 1 Post
Wink

No that is good for the 75 K btu and also good for 3 tons of AC. You say just 14" away try and see if you can line the blower compartment With ductboard insulation it will sure help you here.

ED
 
 