Gas Furnace keeps turning off, blowing cold air....
#1
Gas Furnace keeps turning off, blowing cold air (w/Pix)....
I've got a huge problem. It's freezing outside and I don't have any heat. We went to bed with heat, woke up without heat. I initially thought it was the thermostat so I replaced it with a new one. It didn't seem to fix the problem. I also replaced the filter. I've read through a lot of posts and the suggestion I keep seeing is to sand the flame sensor. I'd be more than happy to do that but I can't seem to find it on my unit.
Problem: furnace starts up and will blow cold air for about 5 minutes and then shut off. it won't come on again unless I hit the reset button. the furnace will start up but only blow cold air for another 5 minutes or so before shutting off. making things worse, the furnace is up in the attic so i've constantly have to go up a ladder.
Furnace: Gas Rheem Criterion. It states it has auto ignite so you don't have to manually turn on the pilot.
Age: ~7 years.
Here are some pictures:
Problem: furnace starts up and will blow cold air for about 5 minutes and then shut off. it won't come on again unless I hit the reset button. the furnace will start up but only blow cold air for another 5 minutes or so before shutting off. making things worse, the furnace is up in the attic so i've constantly have to go up a ladder.
Furnace: Gas Rheem Criterion. It states it has auto ignite so you don't have to manually turn on the pilot.
Age: ~7 years.
Here are some pictures:
Last edited by Seemster; 02-05-05 at 11:35 AM.
#3
Join Date: Jan 2005
Location: Delaware, The First State
Posts: 12,667
Received 39 Upvotes
on
37 Posts
Seemster-URGENT
Is the reset button you are pushing the one pictured under the copper gas line & near the gas valve? If it is, DO NOT CONTINUE TO PUSH IT. This is a flame roll out switch & a safety device. Get a service person to look at this furnace NOW.
#4

Yes I agree with Grady.
That is the only reset button on the furnace.
This trips when there is a crack in the heat exchanger. A crack in this can put carbon monoxide into the house and KILL you.
#6
Thanks for everyone's reply. I really appreciate your feedback. I had a friend who works on commercial systems come by and take a look. We pulled the ignitor out and realized it had short circuited. Bear with me I'm not up with all the correct terminilogy. He was able to fire up the furnace using a match but I was told it would only run for that particular cycle. i'm going to order the part tomorrow. hopefully it'll be here sooner than later but we've got space heaters for the time being. By the way, the thing that I referred to as the reset button is just the door safety switch to make sure the fan stays off while the front panel is off.
here's a pic of the part (To post pictures: [img src="location of image file"/] replace [ ] with < >):
here's a pic of the part (To post pictures: [img src="location of image file"/] replace [ ] with < >):
#10
Join Date: Jan 2005
Location: Delaware, The First State
Posts: 12,667
Received 39 Upvotes
on
37 Posts
Gas Line
As long as we are on the subject of the gas line: My advice is to call a pro & have that copper removed & replaced with black steel pipe. After seeing all of the black flakes in a gas line I replaced last week I was astonished that the furnace still worked. Copper can flake off & get caught under the seat of the gas valve causing it not to seat & gas to leak thru.