Refugee Lp Furnace To Ng

Reply

  #1  
Old 02-14-05, 04:12 PM
m623
Visiting Guest
Posts: n/a
Question Refugee Lp Furnace To Ng

Can you set me right as to the correct orfice replacement to convert an LP furnace used on bottled gas, to NG? I can't seem to make the correct swap.
I don't understand the charts that I have been able to find. The LP orfice is a # 59, and I believe I need a #50,or #51 for NG, but, the chart says that a 51 is just larger than a 1/16" and a 59 is quite a bit smaller. I can slide a 1/16" bit easily thru the #59 that I have. are there different numbers for NG and LP? I'm confused.
any way, the line presure here is 3.5 to 4" of wc. the LP is supposed to flow 12,000 btu
The furnace is a refugee from a travel trailer,forced air burner design from coleman, that I am using to heat my work shop. If I put a stack vent on it, instead of the thru the wall vent, should I use a free breathing setup, like a water heater stack?
Where might I buy numbered drills? What drill size should I use?
If you have answers, or questions, please e-mail me at
email not allowed
Thanks, MIKE
 

Last edited by Ed Imeduc; 02-14-05 at 04:25 PM.
Sponsored Links
  #2  
Old 02-14-05, 04:32 PM
M
Member
Join Date: Dec 2004
Location: San Jose,Ca
Posts: 1,561
Received 1 Vote on 1 Post
Chart shows for a 12,000 burner on nat gas use a 50 drill size. I would probably use a 51 . When you drill out the orifce unless you are using a drill press and holding the orifice absolutely steady there is room for error. I always go a size small and with an adjustable appliance reg you can clock the meter and adjust as needed. Remember if there are multiple orifices you have to divide the number of orifice into the btu rating and drill accordingly. There is plenty of room for error when making conversions. I would recommend checking for c.o after conversion.
 
  #3  
Old 02-14-05, 04:34 PM
Ed Imeduc's Avatar
Member
Join Date: Aug 2002
Location: Mountain Williams Missouri
Posts: 18,389
Received 0 Votes on 0 Posts
Thumbs down

You should go to the maker of the furnace and get a kit for it. In some you have to change the burners also with all the orifice and the gas valve so it has a pressure regulator in it for NTG. THAT #59 LP is for a 12,120 BTU in LP. for the NTG you need a # 50 thats a .0700 drill dia.

AGAIN DONT TRY IT if you dont know gas

ED
 
  #4  
Old 02-14-05, 05:17 PM
M
Member
Join Date: Dec 2004
Location: San Jose,Ca
Posts: 1,561
Received 1 Vote on 1 Post
Ed-- Thank you for mentioning what I should have said. If you are not familar with gas and gas appliances PLEASE think twice about doing this job yourself. This is one area where you can really mess up.
 
  #5  
Old 02-16-05, 08:18 PM
m623
Visiting Guest
Posts: n/a
the orfice seems to only be the tip of the iceberg, LP is OK for now. Thanks for the advice.
MIKE
 
Reply
Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
 
Ask a Question
Question Title:
Description:
Your question will be posted in: