Angry Forced hot air furnace problem -no heat in auto

My T-stat checked fine. I get heat only when the fan is in "ON" and not when in "AUTO". I replaced the Relay and the problem persists. At desired temp, the burner kicks in but the blower comes on only when fan switch is in "ON"! I noticed the limit switch cutting off the the power to the burner when the fan is not blowing and the duct gets too hot. Can somebody help me on this?
 
Sponsored Links
  #2  
Old 11-03-05, 06:42 PM
Member
Join Date: Nov 2005
Posts: 235
Received 0 Votes on 0 Posts
What brand of unit is it?

How old is it?

Standing pilot, or electronic ignition?
 
  #3  
Old 11-03-05, 06:42 PM
Grady's Avatar
Forum Topic Moderator
Join Date: Jan 2005
Location: Delaware, The First State
Posts: 13,936
Received 1 Vote on 1 Post
Fan problem

Either the "heating" speed of your fan motor is gone or whatever control sends power to the fan in the heating mode is malfunctioning. When you put the thermostat in the fan "on" position, it engages the fan in the "cooling" speed regardless if you have A/C or not.
 
  #4  
Old 11-03-05, 07:43 PM
Don Rao
Visiting Guest
Posts: n/a
Talking Forced hot air furnace problem -no heat in auto

My unit is 15 yrs old and it says "Snyder General from Chicago" on the cover plate. I am not sure if the company still exists. I did not realize that only cooling fan comes into play when the fan is in "ON" position. Is the heating fan a low speed or high speed one? If the multispeed fan is gone, is that somethign I (as non technical professional) can replace it myself? If so, I woudl like to try. How much woudl it cost roughly to replace a fan like that? I assume the limit swtich is OK? I just joined this forum today and I am really finding it very productive! Thanks to both of you for your quick responses.
 
  #5  
Old 11-03-05, 07:51 PM
Grady's Avatar
Forum Topic Moderator
Join Date: Jan 2005
Location: Delaware, The First State
Posts: 13,936
Received 1 Vote on 1 Post
Snyder General

Snyder General is now ArcoAire (I think) & a division of ICP which in turn is a division of Carrier.
Easiest way to check if the motor is the problem is to unplug the heating speed wire (usually low [red]) & once the furnace goes off on limit, see if you have 120 volts from the heating speed terminal to ground. If you do, the motor is the problem. If not, there is a control problem.
Replacing the motor is usually not a big deal. Getting the motor off the fan can be the hard part. Check it out & post back in the same thread.
 
  #6  
Old 11-03-05, 08:01 PM
Don Rao
Visiting Guest
Posts: n/a
Talking

Will do and check back tomorrow. Thanks!
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
Display Modes
 
Ask a Question
Question Title:
Description:
Your question will be posted in: