Airlock on oil supply
#1

I had ran out of oil and got a refill but could not get the burner to fire as it kept locking out.
At the tank there is a stopcock and there is another stopcock in the boiler shed,there is a fire valve between the stopcock and the tigerloop.The oil comes as far as the tigerloop but does not enter the glass bowl.....any ideas
At the tank there is a stopcock and there is another stopcock in the boiler shed,there is a fire valve between the stopcock and the tigerloop.The oil comes as far as the tigerloop but does not enter the glass bowl.....any ideas

#2
Join Date: Jan 2005
Location: Delaware, The First State
Posts: 14,403
Received 39 Upvotes
on
37 Posts
Ran out of oil
You probalby are going to have to bleed the pump. There should be a fitting which looks like a grease fitting or a brake bleeder for a car. You will need either a 3/8 or 7/16" wrench & a bottle in which to catch the oil. Start the burner, open the bleeder, & quickly put the bottle in place to catch the oil. If the burner locks out before you get oil, quickly close the bleeder.
You really should get on an automatic delivery program with your fuel supplier.
You really should get on an automatic delivery program with your fuel supplier.
#3
Originally Posted by Grady
You probalby are going to have to bleed the pump. There should be a fitting which looks like a grease fitting or a brake bleeder for a car. You will need either a 3/8 or 7/16" wrench & a bottle in which to catch the oil. Start the burner, open the bleeder, & quickly put the bottle in place to catch the oil. If the burner locks out before you get oil, quickly close the bleeder.
You really should get on an automatic delivery program with your fuel supplier.
You really should get on an automatic delivery program with your fuel supplier.
Would it be possible that some dirt has got stuck where the oil enters the tigerloop as there is no filter on the line.....Many thank's for your reply.
#4
You have no filter at all on the line??
I think it would be time to get an Oil service tech out to put a filter in line, clean the pump (maybe replace), and put in a new nozzel. Then give the burner a complet test/reading.
I think it would be time to get an Oil service tech out to put a filter in line, clean the pump (maybe replace), and put in a new nozzel. Then give the burner a complet test/reading.
#5
Join Date: Jan 2005
Location: Delaware, The First State
Posts: 14,403
Received 39 Upvotes
on
37 Posts
I agree
The installation of a good filter is a must. I actually prefer two filters, one at the tank & the second as close as practical to the inlet of the Tiger Loop.
I do think it is time to call an oil burner tech to check things out.
I do think it is time to call an oil burner tech to check things out.