oil furnace shutting off


  #1  
Old 01-25-06, 02:38 PM
daswede's Avatar
Member
Thread Starter
Join Date: Jul 2003
Location: massachusetts
Posts: 2,218
Likes: 0
Received 0 Likes on 0 Posts
oil furnace shutting off

2-3 times a month my oil fired furnace just shuts off for no apparent reason.
I press the restart button and it comes back on and runs till the next time.
I had it serviced at the beginning of the heating season(oct) and it ran fine till about a month ago. I am going to have a heating tech. look at it,but i want to know what questions to ask,what should be checked,what was the problem?
Any suggestions what might be wrong?
Thanks
 
  #2  
Old 01-25-06, 03:56 PM
bolide's Avatar
Member
Join Date: Jan 2006
Location: PA
Posts: 1,909
Likes: 0
Received 1 Like on 1 Post
Originally Posted by daswede
2-3 times a month my oil fired furnace just shuts off for no apparent reason.
Getting air in oil line, clogged or frozen oil filter, dirty flame sensor, intermittent loss of spark.

Do you have a nice fire when it is working? Or is it burning rough?
 
  #3  
Old 01-25-06, 06:06 PM
daswede's Avatar
Member
Thread Starter
Join Date: Jul 2003
Location: massachusetts
Posts: 2,218
Likes: 0
Received 0 Likes on 0 Posts
Furnace seems to run fine other than shutoffs.
 
  #4  
Old 01-25-06, 06:13 PM
Grady's Avatar
Forum Topic Moderator
Join Date: Jan 2005
Location: Delaware, The First State
Posts: 14,403
Received 39 Likes on 37 Posts
Intermittent shut down

If when you hit the reset button the heater starts with no rumble or smoke, I suspect the start switch on the burner motor is going bad. It is easy to check if the tech knows how.
 
  #5  
Old 01-25-06, 06:52 PM
daswede's Avatar
Member
Thread Starter
Join Date: Jul 2003
Location: massachusetts
Posts: 2,218
Likes: 0
Received 0 Likes on 0 Posts
On manual restart,it briefly rumbles for a second and sounds normal from that point on. After start up there is a smell of oil fumes for awhile but no smoke and the smell goes away.
 
  #6  
Old 01-25-06, 07:06 PM
Grady's Avatar
Forum Topic Moderator
Join Date: Jan 2005
Location: Delaware, The First State
Posts: 14,403
Received 39 Likes on 37 Posts
Rumble

OK, That tells me the burner is trying to start & rules out the motor. The problem could be in the fuel system or the ignition system. On the fuel side it could be dirty. On the igniton system, the transformer could be weak, the electrodes worn or misadjusted or rarely a buss bar could be cracked. Electrode porcelains crack sometimes but resetting will usually not get you running. Let me know what the tech finds.
 
  #7  
Old 01-25-06, 07:18 PM
daswede's Avatar
Member
Thread Starter
Join Date: Jul 2003
Location: massachusetts
Posts: 2,218
Likes: 0
Received 0 Likes on 0 Posts
Thanks bolide and grady,

I will post back with the results when its fixed.
 
  #8  
Old 01-25-06, 07:33 PM
KField's Avatar
Member
Join Date: Dec 2002
Location: Easton, PA
Posts: 3,245
Likes: 0
Received 0 Likes on 0 Posts
I'll put my money on weak ignition or poor electrode setting.

Ken
 
  #9  
Old 01-26-06, 06:01 AM
daswede's Avatar
Member
Thread Starter
Join Date: Jul 2003
Location: massachusetts
Posts: 2,218
Likes: 0
Received 0 Likes on 0 Posts
Great help and advice.
 
  #10  
Old 01-31-06, 03:04 PM
daswede's Avatar
Member
Thread Starter
Join Date: Jul 2003
Location: massachusetts
Posts: 2,218
Likes: 0
Received 0 Likes on 0 Posts
Update as promised:

The problem was a couple of things. (?) The electrodes were not gapped right,
trace of oil on the insulator,and wrong jet nozzel.

Will have to wait and see if this corrects the issue.

Thanks again to all who replied.
daswede
 
 