forced hot air oil burner stopped working
Beckett "AFG" burner with Honeywell "protectorelay" (R8184M-1002) Oil Primary Control. Plenty of oil in the tank, fan motor rotates freely, power vent operates properly, reset (red button) pops up after 45 seconds of no ignition (as it is suppose to). However, the fan motor in the burner unit is not kicking in (as if motor/and primary transformer were getting no power at all) and therefore there is no ignition. No oil is getting into the firebox because the motor is not running. System is 6 years old. I suspect the problem is with the Oil Primary Relay however I want to be sure before I go out and buy a new unit to replace it. Any suggestions?
#2
Member
Join Date: Mar 2006
Location: Wet side of Washington state.
Posts: 16,321
Received 38 Upvotes
on
30 Posts
Originally Posted by Bobby G
Beckett "AFG" burner with Honeywell "protectorelay" (R8184M-1002) Oil Primary Control. Plenty of oil in the tank, fan motor rotates freely, power vent operates properly, reset (red button) pops up after 45 seconds of no ignition (as it is suppose to). However, the fan motor in the burner unit is not kicking in (as if motor/and primary transformer were getting no power at all) and therefore there is no ignition. No oil is getting into the firebox because the motor is not running. System is 6 years old. I suspect the problem is with the Oil Primary Relay however I want to be sure before I go out and buy a new unit to replace it. Any suggestions?
#3
Join Date: Jan 2005
Location: Delaware, The First State
Posts: 12,674
Received 40 Upvotes
on
38 Posts
Bobby G
The problem could be with the power venter. They have safety devices which will not allow the burner to be powered unless there is sufficient draft. Checking orange to white will only tell you there is power out of orange. This usually feeds the venter in one way or another. Power then comes back from the venter assembly to the burner motor. That connection is the place to check for 120 volts.