Unhappy Furnace lights, fan comes on then cuts off too soon

Mom has a model 7670c856 coleman gas furnace, the burner will light, heats, fan comes on, runs about 30 seconds to a minute then shuts off. The burner continues to burn even after fan shuts off, but will go off after a while. The fan unit will not heat the house because the fan will not run long enough. Is this possibly caused by a limit switch, if so which one (high or low)? Please help as she is beginning to get cold.
 
  #2  
Old 10-22-06, 03:28 PM
Jay11J's Avatar
Member
Join Date: Sep 2001
Location: Rochester, Minnesota
Posts: 16,984
Upvotes: 0
Received 0 Upvotes on 0 Posts
What happens if you turn the fan switch (at t-stat or furnace itself) to "ON"?
 
  #3  
Old 10-22-06, 04:00 PM
H
Member
Thread Starter
Join Date: Oct 2006
Posts: 2
Upvotes: 0
Received 0 Upvotes on 0 Posts
The fan will run continually. It was working fine when the a/c was on.
 
  #4  
Old 10-22-06, 04:15 PM
Jay11J's Avatar
Member
Join Date: Sep 2001
Location: Rochester, Minnesota
Posts: 16,984
Upvotes: 0
Received 0 Upvotes on 0 Posts
For now, just leave the fan "ON" for heat..


Sounds like the fan switch is not working like it should.

Part #7710-3281 fan swithc (open85 close105)