Crane oil boiler

Putting a Beckett AF burner on this old Crane boiler. I figure to go with the 97000 water BTU/per hr rating a .75 nozzle would be just about right, what do you guys think.
http://i45.photobucket.com/albums/f98/gonogo/IMG_0359_1_1.jpg
 
  #2  
Old 10-27-06, 09:41 AM
Ed Imeduc's Avatar
Member
Join Date: Aug 2002
Location: Mountain Williams Missouri
Posts: 17,505
Upvotes: 0
Received 1 Upvote on 1 Post
Wink

If I look at that picture I see it call for a 1.25 Nozzle??????? What do you have in the old gun now??? Thats a big jump down to a .75????
Also look and see how the chamber is and what size nozzle and angle it can take.

ED
 
  #3  
Old 10-27-06, 11:59 AM
S
Member
Thread Starter
Join Date: Jan 2005
Posts: 194
Upvotes: 0
Received 0 Upvotes on 0 Posts
A 1.25 nozzle in a Beckett AF input is 175,000 btu, a little on the heavy side I think. I haven’t looked at the other nozzle yet or chamber size, just getting some information together.
 
  #4  
Old 10-27-06, 12:06 PM
Ed Imeduc's Avatar
Member
Join Date: Aug 2002
Location: Mountain Williams Missouri
Posts: 17,505
Upvotes: 0
Received 1 Upvote on 1 Post
Wink

If the other nozzle has been doing good id stay with that kind and size.

ED
 
  #5  
Old 10-27-06, 12:16 PM
S
Member
Thread Starter
Join Date: Jan 2005
Posts: 194
Upvotes: 0
Received 0 Upvotes on 0 Posts
Now this is going from a low speed burner 1750 to the 3450 Beckett AF, so I thought the efficiency of the new burner would be a smaller nozzle for equal BTU’s. I think it would be right to keep the same angle as it has now for chamber size.
 
  #6  
Old 10-27-06, 02:26 PM
Ed Imeduc's Avatar
Member
Join Date: Aug 2002
Location: Mountain Williams Missouri
Posts: 17,505
Upvotes: 0
Received 1 Upvote on 1 Post
Wink

It still comes back to what is the psi of the pump????????????

ED
 
  #7  
Old 10-27-06, 03:26 PM
S
Member
Thread Starter
Join Date: Jan 2005
Posts: 194
Upvotes: 0
Received 0 Upvotes on 0 Posts
The Beckett is 100 psi, no idea what the crane pump pressure is, I would need to put my gauge on it. I don't know of anything that runs less than 100.
 
  #8  
Old 10-27-06, 04:00 PM
Ed Imeduc's Avatar
Member
Join Date: Aug 2002
Location: Mountain Williams Missouri
Posts: 17,505
Upvotes: 0
Received 1 Upvote on 1 Post
Wink

Most new ones run at 125psi now and cut the nozzle a little.
 
  #9  
Old 10-27-06, 08:48 PM
Grady's Avatar
Forum Topic Moderator
Join Date: Jan 2005
Location: Delaware, The First State
Posts: 12,667
Received 39 Upvotes on 37 Posts
Crane/Beckett

IF the burner is new & the pump pressure is set at anything other than 100#, there will be a sticker on it stating the pump pressure setting.

If you are firing @ 1.25 with the old burner, I don't think I would drop any lower than 1.00 - 1.10 gph with the new burner.
 
  #10  
Old 10-28-06, 02:21 AM
S
Member
Thread Starter
Join Date: Jan 2005
Posts: 194
Upvotes: 0
Received 0 Upvotes on 0 Posts
Thanks Ed and Grady. Rechecking the .75 would not be enough btu’s at 100 psi, it would need to be 140 psi, too much for a Beckett AF.
Grady you think the 1 gph at input of 140,000 btu would not be too high for water rating of 97,000 btu.
 
  #11  
Old 10-28-06, 10:48 AM
H
Member
Join Date: Oct 2006
Location: USA
Posts: 56
Upvotes: 0
Received 0 Upvotes on 0 Posts
Originally Posted by slls
Thanks Ed and Grady. Rechecking the .75 would not be enough btu’s at 100 psi, it would need to be 140 psi, too much for a Beckett AF.
Grady you think the 1 gph at input of 140,000 btu would not be too high for water rating of 97,000 btu.
The pumps that come as standard on a Beckett AF burner used to be Suntec A2VA7116, and more recently Beckett CleanCut, These pumps are rated to be adjustable from 100-200psig within the range you are fireing. The AF burner has no restictions as to the pump pressure and belive me, the pump has no clue what kind of burner it is bolted to.

Secondly, Consider the thermal efficiancy of this boiler, the input is 175,000 btuh and the IBR net rating is 97,000, compare that to a newer design boiler at 175,000, the net rating would be 131,000 (ref Peerless WBV4) at todays energy prices I would not sink any more money into such a unit.
 
  #12  
Old 10-28-06, 12:07 PM
S
Member
Thread Starter
Join Date: Jan 2005
Posts: 194
Upvotes: 0
Received 0 Upvotes on 0 Posts
The Beckett AF is free, only cost is new nozzle.
 
  #13  
Old 10-28-06, 06:56 PM
Grady's Avatar
Forum Topic Moderator
Join Date: Jan 2005
Location: Delaware, The First State
Posts: 12,667
Received 39 Upvotes on 37 Posts
slls

You are confusing input & output. The 97k is output with an input of 1.25 gph (175,000 btu/hr). This 97,000 takes into account the combustion efficiency of the burner/boiler, the boilers ability to transfer heat from the flame to the water, & heat loss thru the jacket etc. Hopefully Hello will correct me if I am mistaken but as I understand I=B=R ratings, they reflect only that heat which is available to be put thru the pipes.
In a nutshell, no, I don't think 1.00-1.10 would be too much.

Hello, your thoughts?
 
  #14  
Old 10-29-06, 11:04 AM
S
Member
Thread Starter
Join Date: Jan 2005
Posts: 194
Upvotes: 0
Received 0 Upvotes on 0 Posts
I get it now, what confused me was the amount of input needed on this boiler to get water to 97,000. I had a furnace from that era that was a lot more efficient than this Crane.
I am learning some about boilers, never had to opportunity to work on one until now, it’s for my daughter.
I am going to try the one gph and use the angle and type of the one already installed. I figure the angle in there now will be a match for the combustion chamber. What do you think?
 
  #15  
Old 10-30-06, 10:03 AM
Ed Imeduc's Avatar
Member
Join Date: Aug 2002
Location: Mountain Williams Missouri
Posts: 17,505
Upvotes: 0
Received 1 Upvote on 1 Post
Wink

If it has been working right for the chamber. For sure stay with the spray angle and also with a type A or B nozzle

ED
 
  #16  
Old 10-30-06, 11:52 AM
S
Member
Thread Starter
Join Date: Jan 2005
Posts: 194
Upvotes: 0
Received 0 Upvotes on 0 Posts
Thanks Ed.
 
  #17  
Old 12-09-06, 11:09 AM
S
Member
Thread Starter
Join Date: Jan 2005
Posts: 194
Upvotes: 0
Received 0 Upvotes on 0 Posts
Update : Installed the Beckett AF in the old boiler. The nozzle in it was a 1.0 gal, the local burner man told me to use a .75 to replace. Replaced F6 cap with a F3. Wired by the old stack switch, jumpered the TT on the burner and been going good ever since. Thanks for the reply’s.
 
  #18  
Old 12-18-06, 07:34 PM
KField's Avatar
Member
Join Date: Dec 2002
Location: Easton, PA
Posts: 3,015
Upvotes: 0
Received 0 Upvotes on 0 Posts
I'm coming into this way late but you did exactly what I was about to suggest. The 1.25 gph nozzle was for a burner that was lucky to achieve 75% efficiency. When the rule of thumb was 100,000btus net for 1gph. Now it is more like 121,000btus for 1gph. I would have recommended the .75 and would have advised against the F6 head. That head is worthless unless you are firing between 1.25 and 1.65 in my opinion. The F3 is the best choice for your firing rate. You also might consider using the low firing rate baffle in the burner. It may help slow the flue gasses through the giant open heat exchanger in that boiler. All in all, I'm glad things are working properly.

Ken
 
  #19  
Old 12-19-06, 09:39 AM
S
Member
Thread Starter
Join Date: Jan 2005
Posts: 194
Upvotes: 0
Received 0 Upvotes on 0 Posts
Thanks for the reply, was wondering about the low firing rate baffle. It's going good so I think I will let it go for now.
You are right that is a monster, daughter is not in a position to replace the unit at this time. I would think it is a very wasteful unit to supply hot water in the summer.
 
 