Oil burner, flame pulses
#1
Member
Thread Starter
Join Date: Dec 2006
Location: Pittsburgh
Posts: 2
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Oil burner, flame pulses
Hello, new to this site. My problem is i have a ThermoPride 0H-5 oil furnace that the fire will cutout for about a second or maybe less. It re-ignites just fine, but this creates a pressure condition which bangs my draft regulator.So far i have changed the nozzle,and the inline filter. I cleaned the striner on the pump, and i checked my tank for water. This is a two pipe system as i have a buried tank. The furnace is approx 11 years old.
This problem is driving me nuts as it happens probably 100+ time through a run cycle and it will wake me up often. Any help would be greatly appreciated
This problem is driving me nuts as it happens probably 100+ time through a run cycle and it will wake me up often. Any help would be greatly appreciated
#3
Either high vacuum on the suction line or an air leak. Replace the oil filter with a spin-on with a vacuum gaige and install a Tigerloop. That will eliminate a ton of future headaches and will make it easier to troubleshoot.
Ken
Ken
#5
Join Date: Jan 2005
Location: Delaware, The First State
Posts: 12,667
Received 39 Upvotes
on
37 Posts
Tiger Loop
The Tiger Loop replaces the return line. The advantages are several. There is a reduction in flow which in turn reduces vaccum & improves filtration. There is also the added benefit of burning warm fuel in the case of an outdoor tank.