arcoaire condensation


  #1  
Old 02-08-07, 08:41 AM
M
Member
Thread Starter
Join Date: Feb 2007
Posts: 1
Likes: 0
Received 0 Likes on 0 Posts
arcoaire condensation

My combustion blower keeps filling up with water. I take it out and drain all water from it and replace it. Runs fine for an hour or so and fills up with water again. I have checked trap and drain hoses and they are clear of obstructions. What could be the problem?
 
  #2  
Old 02-08-07, 06:10 PM
HVACGuy's Avatar
Member
Join Date: Jan 2007
Location: Upstate New York
Posts: 134
Likes: 0
Received 0 Likes on 0 Posts
I'm assuming you have a 90% gas furnace?
Check that he hose coming from the bottom of the heat exchanger cover doesn't go uphill before down to the trap. This will stop it from draining & trip out the pressure proving switch.
 
 