Help with Lennox furnace
Old 09-24-07, 10:24 AM
Z
I have a Lennox furnace/AC that has worked fine for 7 years but this weekend the batteries went dead in my Honeywell/35thermostat and now nothing works. I have changed those batteris other times with no problem but I don't think they ever died before.
The thermostat appears to be working, all of the information such as time, setpoints, etc. appear normal and it seems to click when I change the setpoint above the room temp. But neither the furnace or the AC work. I cannot even turn on the fan manually from the stat.
Everything worked fine until those batteries died so the prob must be with that thermostat but I am at a loss as to what it might be.
The Lennox furnace has neither of those diag lites on. I have never seen both of them off before. When I push in the interlock (with the panel off) I hear a hum so I am guessing the power is there.
Any help would be appreciated.............
Old 09-24-07, 05:47 PM
D
when you took the thermostat off to replace the batteries, any chance that a wire at the thermostat came loose or broke off? look at the wiring teminals at the thermostat, you should see terminals R,G,Y,W. try a jumper wire from R to G it should start the inddor fan, a jumper from R to W should start the heating cycle
Old 09-24-07, 06:50 PM
Ed Imeduc's Avatar
Wink
Some furnace units have a small fuse on the board In them . Have you checked that out?????
Old 09-28-07, 09:29 AM
Z
Thanks for the responses to my request for help.
The theromstat checked out okay. I had a service call from the vendor who installed the furnace/AC and he checked out the thermostat.
I think the batteries getting low was a red herring. My wife had noticed the A/C has stopped working before she changed the batteries and that is why she noticed the low battery inidcation and changed them.
Turns out there is a small 24V breaker inside the furnace enclosure on a PC board that was tripped. He reset it and the furnace started. (only $89.95 for that service)
He did not however fully check the unit because had he done so he would have found that the A/C trips the breaker and not the furnace. So I have another call into them for another look at it. Hope it don't cost me another $89.95 for the second look! Being an A/C unit it may very well be a lot more then that though.
Any idea why the A/C trips the common 24V thermostat breaker? As long as the furnace is working the breaker does not trip but as soon as the A/C is selected at the thermostat the breaker trips.
Thanks..............
Old 09-28-07, 11:58 AM
D
It's probably an issue with the control wiring going to the outdoor unit or a component inside the outdoor unit that has failed [for example- the contactor]. Take a look at the wires at the outdoor unit, you should see a small cable. Maybe it was hit by a weed wacker or a critter chewed it? The technician should have verified that all parts of your system were working. Circuit breakers don't normally trip for no reason
Old 10-01-07, 11:19 AM
Z
Bingo! You hit the nail on the head. The tech came and found a shorted wire on the outside unit. I think I remember slightly moving that unit when I was painting the house so that little shove probably cost me a total of $315.00 dollars to get repaired.
On the bright side he said that the PC board costs $900.00 to have replaced and the compressor costs $1500.00! Maybe he was just trying to make me feel better about paying $315.00 to replace a wire. Boy I must have been in the wrong business all of my life!
Thanks for the responses............