Moffat J-Line problems

Hi, I am new to this forum and was wondering if anyone could help me figure out a problem I have with my furnace. It is an older Moffat J-line gas forced air furnace, and the problem is that the furnace fan does not shut off when the furnace has cooled down. It runs continuously. I have had some success by giving the furnace a whack on the outside cowling out of sheer frustration, but the problem always comes back. The summer fan switch is set to off. Any help would be appreciated to rectify this problem.

Thanks.
 
Sponsored Links
  #2  
Old 09-26-07, 06:08 PM
S
Member
Join Date: Oct 2006
Location: Dayton area GO Bucks!
Posts: 101
Received 0 Votes on 0 Posts
I am new to this forum and was wondering if anyone could help me figure out a problem I have with my furnace. It is an older Moffat J-line gas forced air furnace, and the problem is that the furnace fan does not shut off when the furnace has cooled down. It runs continuously. I have had some success by giving the furnace a whack on the outside cowling out of sheer frustration, but the problem always comes back.

Never heard of a Moffat J-line, but it sounds like you have a fan/limit control that's out of calibration or bad. You can try and adjust the control, but it might be best to replace the control. The control has several types of shapes and sizes so if you can post a picture of the furnace we can give a more detailed instructions.
 
  #3  
Old 09-26-07, 10:13 PM
R
Member
Thread Starter
Join Date: Sep 2007
Posts: 3
Received 0 Votes on 0 Posts
Moffat J-Line pics

Not sure how to post a picture on here.
 
  #4  
Old 09-27-07, 08:51 AM
Ed Imeduc's Avatar
Member
Join Date: Aug 2002
Location: Mountain Williams Missouri
Posts: 18,389
Received 0 Votes on 0 Posts
Wink

Check and see if you have a wire schematic on the blower door. If you dont find a control like said. That you can set . You might Look for a round klixon fan control. They go bad and you have to put a new one in then. Some times if you have a pilot that is on all the time. This will keep the blower on when it still like warm out.
 
  #5  
Old 09-27-07, 03:37 PM
D
Member
Join Date: Aug 2007
Posts: 2,021
Received 0 Votes on 0 Posts
Originally Posted by Ed Imeduc View Post
Check and see if you have a wire schematic on the blower door. If you dont find a control like said. That you can set . You might Look for a round klixon fan control. They go bad and you have to put a new one in then. Some times if you have a pilot that is on all the time. This will keep the blower on when it still like warm out.
look at the control itself and see if you can find a brand name [like Honeywell or Cam Stat] and also a model or part #. If the control has 3 or 4 wires it's probably a combination fan and limit control. easy to replace and not too expensive. if it's type that inserts the sensing element into a hole in the furnace, be sure the sensing element on the new one is the same length [HW L4064B controls come in 5, 8 or 11 inch models, about $52 at arnold's hvac parts online]. let us know what you find.
 
  #6  
Old 09-27-07, 09:53 PM
R
Member
Thread Starter
Join Date: Sep 2007
Posts: 3
Received 0 Votes on 0 Posts
J-line probs.

Thanks for the info. Youve been a great help. I'll let you know whats what.
 
Reply
Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
 
Ask a Question
Question Title:
Description:
Your question will be posted in: