Exclamation lights with a boom

Our old natural gas furnace in the garage sometimes lights rather alarmingly. It seems slow to ignite and sometimes it blow flames out of the front when it finally lights with a boom. What are the probable causes. Is it the gas valve or the mixture settings or ? I can get you the make and model if that will help.
 
Sponsored Links
  #2  
Old 09-30-07, 05:10 PM
KField's Avatar
Member
Join Date: Dec 2002
Location: Easton, PA
Posts: 3,245
Received 0 Votes on 0 Posts
Many times it is an ignitor placement or alignment problem. Any good service tech should be able to get it working correctly on an annual tune-up.

Ken
 
  #3  
Old 10-01-07, 03:31 PM
E
Banned. Rule And/Or Policy Violation
Join Date: May 2007
Location: Wisconsin
Posts: 8,629
Received 0 Votes on 0 Posts
If the ignition source (spark, or flame) is not right next to an orifice or slits in burners that allow gas to quickly come in contact with the ignition source, due to these being plugged up in the near vicinity, this can cause gas to build up until the gas finally reaches the ignition source, and then it can literally explode into ignition.

You really need to clean or have the furnace cleaned in the burners area. You can buy long round wire brushes for such a purpose. I've seen burner slits get all plugged up with rust and carbon, and when taking the burners out have poured tons of this junk out from the hollow insides!
 
  #4  
Old 10-02-07, 04:38 AM
mattison's Avatar
Member
Join Date: Mar 2003
Location: Cinti, OH
Posts: 5,549
Received 0 Votes on 0 Posts
Like said. Get this thing cleaned and safety checked. It sounds like the crossover tubes are clogged.
 
  #5  
Old 10-02-07, 09:43 PM
Ed Imeduc's Avatar
Member
Join Date: Aug 2002
Location: Mountain Williams Missouri
Posts: 18,389
Received 0 Votes on 0 Posts
Wink

Our old natural gas furnace
Im with Matt Vaccum out the burners and make sure that the pilot ignitor strip is clean. On all burners. check for any spiders in the venturi of the burners and the pilot
 
  #6  
Old 10-03-07, 06:59 PM
user 10's Avatar
Member
Join Date: Mar 2004
Location: NA
Posts: 2,032
Received 39 Votes on 33 Posts
Continuing to operate it like that may result in explosion, fire, and/or death.

If you value your safety more than the cost of a service call, step away from the furnace and find a qualified heating contractor.
 
  #7  
Old 10-05-07, 10:12 AM
T
Member
Thread Starter
Join Date: Jan 2006
Location: Canada
Posts: 32
Received 0 Votes on 0 Posts
I will take a look at it. I am not a bonified service tech (I am a journeyman motor mechanic) but I can handle a cleaning I think, if I am careful (I have watched it being done a few times). That furnace will be replaced soon but I just need to heat the place up a few times to complete a project in the meantime; we will not go away and leave it unattended. Should I go to a heating supply place to get one of the long round brushes; or do they come in a set of sizes? "make sure that the pilot ignitor strip is clean"...What exactly is the 'pilot ignitor strip' and what's the best way to clean that one? "check for any spiders in the venturi of the burners and the pilot"... do you mean rust and crud and dirt and bugs in general, that might be accumulating in the venturi? If the "crossover tubes are clogged", I should be able to clear that all out with the round brush and air and vacuum? I will make sure all of the slits or orifices are clear so the fuel will be directly available at the ignitor, and that the ignitor is aligned. I appreciate the input and the cautionary advice. Is there anything else anyone can think of? Thanks a bunch.
 
  #8  
Old 10-06-07, 08:36 AM
B
Member
Join Date: Jul 2006
Location: Near Philly
Posts: 559
Received 0 Votes on 0 Posts
My 2 cents: I'm not a rich man but I know sometimes it pays to have someone do something who knows what they're doing. This seems to me to be one of those times. I'd pay instead of risking a gas leak explosion or CO2 poisoning due to cracked heat exchanger.
 
  #9  
Old 10-08-07, 09:37 AM
T
Member
Thread Starter
Join Date: Jan 2006
Location: Canada
Posts: 32
Received 0 Votes on 0 Posts
I quite often ask enough 'dumb questions' until it sounds like I am totally incompetent I am sure I can handle a cleaning without killing myself. We have decided though, to let this old furnace go to the grave. Upon further thought, we remember in the past having to 'clobber' the gas valve with the handle of a screwdriver because it was sticking; a cleaning isn't going to give us clear sailing anyway. The new installation will be in a week or two so for the time being (so I can finish my current project) I am going to heat the place up with my propane tiger torch or heater. There is good insulation in there and we aren't into the deep freeze yet. That old dinosaur doesn't get anymore of my time. Thanks a bunch to everybody for your input. I can access the technical info in this thread again in the future as the need arises. Do it yourself is a great furum!
 
Reply
Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
 
Ask a Question
Question Title:
Description:
Your question will be posted in: