Thermal Zone heater problem

Hi everyone,
I have a Thermal Zone furnace and it will not stay running. It blinks 3 times and a code says PRESSURE SWITCH STUCK.
Any ideas what the problem could be? I guess if you blow on it or thru it it will work for a minute...
Thanks for your advice...
 
  #2  
Old 10-26-07, 07:00 PM
D
Member
Join Date: Aug 2007
Posts: 2,021
Upvotes: 0
Received 0 Upvotes on 0 Posts
Originally Posted by Cyndy View Post
Hi everyone,
I have a Thermal Zone furnace and it will not stay running. It blinks 3 times and a code says PRESSURE SWITCH STUCK.
Any ideas what the problem could be? I guess if you blow on it or thru it it will work for a minute...
Thanks for your advice...
Does the combustion air motor start?

Things to check:

cracked switch hose, obstructed switch hose, Bad switch, combustion air fan not running, combustion air fan not running at full speed- IOW bad bearings slowing it down, combustion air fan wheel rotted away or loose on the motor shaft.
Let us know if find anything.
 
  #3  
Old 10-26-07, 07:13 PM
C
Member
Thread Starter
Join Date: Oct 2007
Posts: 3
Upvotes: 0
Received 0 Upvotes on 0 Posts
Thanks for your response but those are all fine, I guess we know it is the pressure switch but don't know if it can be cleaned or has to be replaced. It says PRESSURE SWITCH STUCK CLOSED...
Thanks again
 
  #4  
Old 10-26-07, 07:29 PM
D
Member
Join Date: Aug 2007
Posts: 2,021
Upvotes: 0
Received 0 Upvotes on 0 Posts
Originally Posted by Cyndy View Post
Thanks for your response but those are all fine, I guess we know it is the pressure switch but don't know if it can be cleaned or has to be replaced. It says PRESSURE SWITCH STUCK CLOSED...
Thanks again
usually replaced.
 
  #5  
Old 10-26-07, 07:57 PM
E
Banned. Rule And/Or Policy Violation
Join Date: May 2007
Location: Wisconsin
Posts: 8,627
Upvotes: 0
Received 1 Upvote on 1 Post
Cyndy,

Codes do not always know the root cause though. The pressure switch may be closed, as claimed, but there might be a reason why it is closed, other than a faulty switch.

The pressure switch senses pressure from the drafting/flue process. The pressure in those rubber hoses is extremely minute'.

You were able to make the furnace work by sucking or blowing on it by overriding the natural forces involved. This may or may not mean it is the pressure switch itself. It could be that the pressure is just a hair off, that when the diaghram inside it moves, it is not moving quite enough to engage the electrical contact points.

You may be able to effectively test the diaghram by sucking in or blowing through one of the vacuum tubes and pincing off the hose quickly. If it holds without you either seeing the diaghram's plunger move (you can on some models), or hear it click afterwards - then it is good. But if you see it move, or hear it click after a while of holding the line pinced closed, then it is bad.
 
  #6  
Old 10-26-07, 08:14 PM
C
Member
Thread Starter
Join Date: Oct 2007
Posts: 3
Upvotes: 0
Received 0 Upvotes on 0 Posts
Thanks ecman,
I don't see a diaghram or plunger to test that but blowing in the tube definetely starts it up...
 
  #7  
Old 10-27-07, 01:41 PM
E
Banned. Rule And/Or Policy Violation
Join Date: May 2007
Location: Wisconsin
Posts: 8,627
Upvotes: 0
Received 1 Upvote on 1 Post
Now you just have to do as I suggested so you know if it is indeed the pressure switch itself, or instead if the switch is not responding because the suction or push in the line you blow or suck on is insufficient due to other things like dj suggested in a post below.
 
  #8  
Old 01-30-09, 06:17 PM
Join Date: Jan 2009
Location: CA
Posts: 1
Upvotes: 0
Received 0 Upvotes on 0 Posts
all zones stay on at same time

I have a TZ-3 Honeywell Total zone sys. and all zones stay on. It should be on each station until it reaches temp then switch to the next... it doesn't.
 
 