Old 12-02-07, 03:33 PM
Member
Thread Starter
Join Date: Dec 2007
Posts: 4
Received 0 Votes on 0 Posts
4minute shutdown for Rudd Gas Furnace

I have a 1990? Rudd gas furnace Model UGKA 10EA GS, serial number NN5D307 F0940 4643 with Robert Shaw controller 100-00812 (34PL 308A) call for heat starts draft blower which runs 20 sec, HSI glows 15 seconds, gas valve opens and burner ignites. HSI turns off and furnace and blower run fine for about
4 minutes and then gas valve shuts off. Exhaust blower continues to run and the whole cycle repeats 3 times (I think).There is no remote flame sensor to clean, How does the control board know that the burner is on? Why does the valve stay open for 3 or 4 minutes and then shut off? Do I need a new control board?
 
Sponsored Links
  #2  
Old 12-02-07, 04:20 PM
Grady's Avatar
Forum Topic Moderator
Join Date: Jan 2005
Location: Delaware, The First State
Posts: 13,936
Received 1 Vote on 1 Post
Does the circulating fan come on? Is the air filter clean & all registers open & not blocked? What type of thermostat?
 
  #3  
Old 12-02-07, 04:41 PM
Member
Join Date: Aug 2007
Posts: 2,021
Received 0 Votes on 0 Posts
It sounds like what you're saying is the burners lite, the circulating fan runs for about 4 minutes, then it shut off and very shortly afterwrds the burner goes off? Is that the sequence you are experiencing?
 
  #4  
Old 12-03-07, 10:05 AM
boilersrus's Avatar
Member
Join Date: Nov 2007
Location: Long Island, NY
Posts: 313
Received 0 Votes on 0 Posts
Most hard disk ignitors also are used as a flame sensor too. They are bi-directional, they heat up with current when energized, then when they are not energized they send a signal back to the brain (controller) to let it know that the main burners are on. I would remove the HDI and examine it real closely for pitting, cracks, chips. I would say that there is probably more than a 75% chance of it being bad. One more thing, I bet that the problem doesn't happen ALL the time, right? Good luck. Charlie
 
  #5  
Old 12-03-07, 08:18 PM
Member
Join Date: Nov 2007
Posts: 36
Received 0 Votes on 0 Posts
http://www.myhvacparts.com/Catalogue...%20Control.htm


is this your ignition control board?
place i found it is just a random search. i do not know this place at all.
 
  #6  
Old 12-04-07, 01:06 PM
Member
Thread Starter
Join Date: Dec 2007
Posts: 4
Received 0 Votes on 0 Posts
20 minutes shut down for Gas furnace

I found one problem, a bad connection to the door switch. I fixed that, cleaned the air filter, checked all the electrical connections. Furnace now runs up to 20 minutes and then the gas valves clicks on and off very rapidly 2 to four times and then the burner goes out. The exhaust blower and the circulating blower continues to run (indefinitely?). If the power is turned off and back on, the normal ignition sequences starts and everything runs normally for another 20 minutes. I also noticed that once the thermostat reaches the proper temperature the burner shuts off, the circulating fan shuts off after a few minutes but the exhaust blower continues to run indefinitely. Is the exhaust blower relay sticking in the closed position? Can the relay be cleaned or do I need to replace it? Where is the relay? On the Ignition control board or on the circulating blower control board?
 
  #7  
Old 12-04-07, 01:35 PM
Member
Join Date: Aug 2007
Posts: 2,021
Received 0 Votes on 0 Posts
Tell us about the thernostat. Is it digital? What is the brand and model#
 
  #8  
Old 12-04-07, 04:30 PM
Grady's Avatar
Forum Topic Moderator
Join Date: Jan 2005
Location: Delaware, The First State
Posts: 13,936
Received 1 Vote on 1 Post
Ignition Control Board

Does the board have any kind of diagnostic light which blinks a code when the gas valve clicks & shuts down?
 
  #9  
Old 12-04-07, 09:27 PM
Member
Join Date: Nov 2007
Posts: 36
Received 0 Votes on 0 Posts
put a voltmeter on the com and 24v of the gas valve. whats it doing when it flickers?
 
  #10  
Old 12-09-07, 12:05 AM
Member
Thread Starter
Join Date: Dec 2007
Posts: 4
Received 0 Votes on 0 Posts
4 minute shutdown for Rudd gas furnace

Thanks for all your help. I tried all your suggestions but to no avail. I purchased a replacement White Rodgers HSI control board and the ignition problems are all solved.
Thanks very much for your input I appreciate it very much.
God bless you all,
Gene
 

Last edited by genew; 12-09-07 at 12:06 AM. Reason: Typos
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
Display Modes
 
Ask a Question
Question Title:
Description:
Your question will be posted in: