Coleman Furnace

Hi Tim here I have a Robert Grayson control on a coleman propane furnace and the pilot will only stay ignited if I hold the start button down and the flame is very weak.
 
Sponsored Links
  #2  
Old 12-25-07, 11:11 AM
Grady's Avatar
Forum Topic Moderator
Join Date: Jan 2005
Location: Delaware, The First State
Posts: 13,936
Received 1 Vote on 1 Post
Coleman Propane

If you have plenty of gas, remove & clean the pilot burner. You could have some carbon or rust partially plugging the orifice.
 
  #3  
Old 12-26-07, 06:44 PM
pflor's Avatar
Member
Join Date: Dec 2007
Location: U.S.A.
Posts: 1,127
Received 0 Votes on 0 Posts
And if after following Grady's advice to the letter the pilot flame is still weak, maybe the thermocouple is bad.

Now...I assume we have a thermocouple here. Is it possible that the thermocouple connection at the gas valve may have become loose? You'll need a small adjustable wrench to tighten it. If tight, the thermocouple itself could be bad; when was the last time it was replaced? they go for about $5, a modest investment, go for it.
 
  #4  
Old 12-27-07, 06:02 PM
Grady's Avatar
Forum Topic Moderator
Join Date: Jan 2005
Location: Delaware, The First State
Posts: 13,936
Received 1 Vote on 1 Post
Thermocouple

The thermocouple would have nothing to do with the intensity of the pilot flame. It is simply a heat powered generator.
 
  #5  
Old 12-27-07, 06:23 PM
pflor's Avatar
Member
Join Date: Dec 2007
Location: U.S.A.
Posts: 1,127
Received 0 Votes on 0 Posts
true indeed...but if the pilot flame is weak, the thermocouple won't get hot enough, won't produce enough electricity and the safety shutoff valve would turn the gas valve OFF.
 
  #6  
Old 12-27-07, 07:13 PM
SeattlePioneer's Avatar
Banned. Rule And/Or Policy Violation
Join Date: Jul 2007
Location: Seattle, Wa
Posts: 5,503
Received 0 Votes on 0 Posts
Originally Posted by Thill View Post
Hi Tim here I have a Robert Grayson control on a coleman propane furnace and the pilot will only stay ignited if I hold the start button down and the flame is very weak.
As in so many of these problems, correct diagnosis of the problem is the key. As suggested in earlier posts, a good pilot flame is essential ---- is the pilot flame blue and does it engulf the thermocouple it points at? It should usually look like a small sharp flame, not subject to being blown around like a candle flame.


If the pilot flame is good, you really need an adaptor to measure the millivolts being produced by the thermocouple. If the millivolts are 10-15 or so and the pilot wont stay lit, you probably have an electric gas valve that needs to be replaced. If you get 0-10 millivolts, it's probably the thermocouple that needs replacement.


This is straightforward troubleshooting for any furnace repairman. If you don't have the tools and parts, you are better off calling someone in.

One reason for that is that the whole funace should be inspected for maintenance needs, from fileter replacement to inspecting the heat exchanger and cleaning burners and checking the chimney for proper operation.


More than likely this can all be done for an hour labor charge or so. Fix only the pilot problem and you may neglect other problems that will cost you more money or be a hazard.
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
Display Modes
 
Ask a Question
Question Title:
Description:
Your question will be posted in: