My Lennox G40 model furnace switches to Watchguard sporadically. It is only 7 years old. It prevents the heater unit from lighting. I reset the system and it will fire up the furnace just fine.
What triggers the Watchgaurd?
What is it trying to tell me?
What should I be checking?
The system will heat the house fine whenever it want to, however, it will go to watchguard overnight. During the daytime it seems to do this less often.
What triggers the Watchgaurd?
What is it trying to tell me?
What should I be checking?
The system will heat the house fine whenever it want to, however, it will go to watchguard overnight. During the daytime it seems to do this less often.
#2
Member
Join Date: Jan 2009
Posts: 5
Upvotes: 0
Received 0 Upvotes
on
0 Posts
same issue here
I have a G60DFV(X) Lennox that is doing the exact same thing. Mine is only 4 years old.
I am reading and learning about these things every minute. I have checked some basics like the primary limit switch and the flame rollout sensors, but I think my next step is to remove the flame sensor and clean it with steel wool.
I will let you know what I come up with.
there seems to be a number of things that can cause the Watchguard mode to engage...
I have a similar thread going, check here to see if anybody has more info
http://forum.doityourself.com/gas-oi...ml#post1499390
I am reading and learning about these things every minute. I have checked some basics like the primary limit switch and the flame rollout sensors, but I think my next step is to remove the flame sensor and clean it with steel wool.
I will let you know what I come up with.
there seems to be a number of things that can cause the Watchguard mode to engage...
I have a similar thread going, check here to see if anybody has more info
http://forum.doityourself.com/gas-oi...ml#post1499390
#4
As I understand it, the Watchguard lockout can be caused by a wide variety of problems:
A: Burners failed to ignite
B: Limit open more than 3 minutes
C: Lost flame sense 5 times in one heating cycle
D: Pressure switch opened 5 times in one heating cycle
Jg, it's rapidly becomes confusing to try to discuss different problems on the same thread. I'd like to suggest you start a new thread.
You have a good description of what is happening with your furnace on the link.
And doit---
As Skip suggested, you need to identify what is quitting before the Watchguard lockout. Before it locks out it typically identifies problems and you can probably observe how far along in the start up sequence the furnace gets before it quits.
A: Burners failed to ignite
B: Limit open more than 3 minutes
C: Lost flame sense 5 times in one heating cycle
D: Pressure switch opened 5 times in one heating cycle
Jg, it's rapidly becomes confusing to try to discuss different problems on the same thread. I'd like to suggest you start a new thread.
You have a good description of what is happening with your furnace on the link.
And doit---
As Skip suggested, you need to identify what is quitting before the Watchguard lockout. Before it locks out it typically identifies problems and you can probably observe how far along in the start up sequence the furnace gets before it quits.
#5
Member
Join Date: Jan 2009
Posts: 5
Upvotes: 0
Received 0 Upvotes
on
0 Posts
thanks Skip, I will try to catch the code prior to the furnace going into Watchguard mode.