Utility brand, model B.75 FAF Stays on?

The furnace is a Utility brand, model B.75 FAF. The thermostat is a Hunter
"Set n' Save" model.

I turn the thermostat down during the day, but the heater stays on for about 15 more minutes or it stays on, goes off and comes back on then shuts down and stays down until I turn the
thermostat on.

Is it a defective thermostat?

Thanks
 
  #2  
Old 03-15-08, 04:19 AM
Jay11J's Avatar
Member
Join Date: Sep 2001
Location: Rochester, Minnesota
Posts: 18,427
Received 0 Votes on 0 Posts
What happens when you set system swtich from Heat to OFF? If nothing happens, then it's the t-stat.

FYI, get a good stat like Honeywell. Hunters stats are not the best out there.
 
  #3  
Old 03-16-08, 01:23 AM
P
Member
Thread Starter
Join Date: Mar 2008
Posts: 2
Received 0 Votes on 0 Posts
Originally Posted by Jay11J View Post
What happens when you set system swtich from Heat to OFF? If nothing happens, then it's the t-stat.

FYI, get a good stat like Honeywell. Hunters stats are not the best out there.

Thank you!! I put in a Honeywell and everything is fine now.

Again thanks!!
 
  #4  
Old 03-16-08, 05:00 AM
Jay11J's Avatar
Member
Join Date: Sep 2001
Location: Rochester, Minnesota
Posts: 18,427
Received 0 Votes on 0 Posts
I'd like to suggest, on the set up menu of the t-stat, set the stat to 3, either it wil say "Hot water heat or High Eff.", or CPH.
 
 