Tempstar furnace problem

Reply

  #1  
Old 10-20-08, 04:29 AM
Member
Thread Starter
Join Date: Oct 2008
Location: pittsburgh
Posts: 4
Tempstar furnace problem

I have a tempstar NG forced air furnace that when thermostat calls for heat, Ignitor clicks, lights the pilot, burners come on for approx 20 to 30 seconds then they go out, and cycle starts again. Pilot stays lit and does not go out.

Could the gas control valve be bad or would the ignition module be the problem??

Thanks in advance for any help.

John
 
Sponsored Links
  #2  
Old 10-20-08, 04:50 AM
mattison's Avatar
Member
Join Date: Mar 2003
Location: Cinti, OH
Posts: 5,549
More than likely it's the flame sensor. With the furnace off, remove the cover to expose the burner area. Usually on the far left side there is a rod about 3" long extending into the burner area to sense flame. Clean it off with a scotch brite pad and try your furnace again.
 
  #3  
Old 10-20-08, 05:16 AM
Member
Thread Starter
Join Date: Oct 2008
Location: pittsburgh
Posts: 4
Thanks for the tip. I will clean the sensor. In the event this does not rectify the issue, what would be the next item to check???
 
  #4  
Old 10-21-08, 07:14 AM
Member
Thread Starter
Join Date: Oct 2008
Location: pittsburgh
Posts: 4
I found the sensor and cleaned it. Problem solved, and much faster ignitor operation. It turned out that the ignitor and flame sensor are all in one. Thanks for the help.
 