Pilot light doesn't stay lit

I've done ALOT of reading and think that I have my problem figured out, just want to run it by you all here.

Pilot light was lighting but was weak, cleaned pilot tube, and orifice, now have a good flame. Gas turned to on but pilot light goes out when thermostat calls for heat. Replaced thermocouple with a new one, same problem exists. I am suspecting my control valve is bad.

OLD Carrier unit with Essex SX211 control valve:
211-221000-1307B
I-8 set> 3.5 in.> 3 cu. ft. filter> 25V 60hz> Time delay open>
Cust No, Q1.3590C
Any ideas where to source one, or am I on the wrong track.

Any help you can provide will be greatly appreciated.
Rob
 
Sponsored Links
  #2  
Old 10-23-08, 04:25 PM
Banned. Rule And/Or Policy Violation
Join Date: May 2007
Location: Wisconsin
Posts: 8,629
Received 0 Votes on 0 Posts
What lights the pilot? Or do YOU have to light it? If you do, then it has a pilot setting? And if left there, let's say, the pilot will stay on? But as soon as you switch it to ON, with a call for heat, the pilot then goes out?

And IF this is right so far, does the burner come on, even for a split second, and snuff out the pilot? Or does simply the call for heat snuff it before any burner even comes on?
 
  #3  
Old 10-23-08, 05:04 PM
Member
Join Date: Dec 2004
Location: San Jose,Ca
Posts: 1,561
Received 0 Votes on 0 Posts
Originally Posted by dominoid View Post
I've done ALOT of reading and think that I have my problem figured out, just want to run it by you all here.

Pilot light was lighting but was weak, cleaned pilot tube, and orifice, now have a good flame. Gas turned to on but pilot light goes out when thermostat calls for heat. Replaced thermocouple with a new one, same problem exists. I am suspecting my control valve is bad.

OLD Carrier unit with Essex SX211 control valve:
211-221000-1307B
I-8 set> 3.5 in.> 3 cu. ft. filter> 25V 60hz> Time delay open>
Cust No, Q1.3590C
Any ideas where to source one, or am I on the wrong track.

Any help you can provide will be greatly appreciated.
Rob
I'm reading this....you light the pilot and you let up on the knob to turn to on position and pilot goes out,,right? If yes the valve power unit is bad and the valve needs to be replaced. That isn't uncommon for those Essex valves.
 
  #4  
Old 10-23-08, 10:55 PM
Member
Thread Starter
Join Date: Oct 2008
Location: OK
Posts: 3
Received 0 Votes on 0 Posts
When gas is turned to the "on" position it will stay lit, until the thermostat calls for heat, then the pilot goes out immediately the burner does not ignite at all. I put a multimeter on the solenoid valve and it has 24V at the point the pilot goes out.
 
  #5  
Old 10-24-08, 12:38 PM
Member
Thread Starter
Join Date: Oct 2008
Location: OK
Posts: 3
Received 0 Votes on 0 Posts
Replaced valve with a Robertshaw 700-402, works like a CHAMP!!
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
Display Modes
 
Ask a Question
Question Title:
Description:
Your question will be posted in: