Smartvalve lights pilot not main burners

Reply

  #1  
Old 10-30-08, 01:15 PM
Member
Thread Starter
Join Date: Oct 2008
Location: Oklahoma
Posts: 11
Smartvalve lights pilot not main burners

Smartvalve lights pilot not main burners

I have a NG Arcoaire furnace, with ST9120C 4057 Fan Control and a SV9501M 2056 Smartvalve.

When I call for heat, inducer motor starts and the hot surface igniter lights the pilot. Blue flame is visible.
The sequence is stuck there, and eventually the pilot goes out and tries again in a couple of minutes.

Main burners just wont light. I jumpered pins 1 and 6 on the board's 6-pin Molex connector to bypass the limit switch, but no luck.
 
Sponsored Links
  #2  
Old 10-30-08, 01:23 PM
mattison's Avatar
Member
Join Date: Mar 2003
Location: Cinti, OH
Posts: 5,549
Smartvalve is the problem. They are notorious for going bad.
 
  #3  
Old 10-30-08, 01:36 PM
Member
Thread Starter
Join Date: Oct 2008
Location: Oklahoma
Posts: 11
Originally Posted by mattison View Post
Smartvalve is the problem. They are notorious for going bad.
Do you have a suggestion?
 
  #4  
Old 10-31-08, 10:58 AM
Member
Thread Starter
Join Date: Oct 2008
Location: Oklahoma
Posts: 11
Exclamation

Any other testing or workarounds I might have missed before I blindly replace a $200 part?

I was of the understanding that smartvalves were the state-of-the-art, any thoughts?
 
  #5  
Old 10-31-08, 11:40 AM
mattison's Avatar
Member
Join Date: Mar 2003
Location: Cinti, OH
Posts: 5,549
Check for 24VAC at the gas valve with a call for heat. If it's there then the valve is shot. Sometimes you can just play with the wires at the gas valve with a call for heat and it will start working. They are junk.
 
  #6  
Old 10-31-08, 01:52 PM
Member
Thread Starter
Join Date: Oct 2008
Location: Oklahoma
Posts: 11
Originally Posted by mattison View Post
Check for 24VAC at the gas valve with a call for heat. If it's there then the valve is shot. Sometimes you can just play with the wires at the gas valve with a call for heat and it will start working. They are junk.
With Pin 1 as common (on the 4-pin connector), I have 24vac at both pins 2 and 3, and an inconclusive (possibly floating) voltage at pin 4.

Any alternatives to buying another 'junk' smartvalve as a replacement?
 
  #7  
Old 10-31-08, 07:15 PM
Member
Join Date: Dec 2005
Posts: 458
The smart valve was a great idea in theory. The flame sensor may need to be cleaned. I would try that before replacing the valve. A pilot/flame rod assembly is alot cheaper than a valve.
 
  #8  
Old 10-31-08, 08:03 PM
Member
Thread Starter
Join Date: Oct 2008
Location: Oklahoma
Posts: 11
Originally Posted by thermofridge View Post
The smart valve was a great idea in theory. The flame sensor may need to be cleaned. I would try that before replacing the valve. A pilot/flame rod assembly is alot cheaper than a valve.
Thanks, Ill give that a try when it's daylight.
Is scotchbrite too rough for cleaning?
 