Furnace burner will not ignite

Hello Guys,
How all doing?

System: Carrier 8000ST
When Heat was Turn ON
1. blower power up for a couple min.
2. system call for heat (inducer)

Burner wont ignite.
According to led code: It is low heat pressure switch problem.

My question:
Is there other possibility? and how do testing the pressure switch by using the ohm meter?

Thanks for your help
Tran
 
Sponsored Links
  #2  
Old 11-19-08, 08:19 PM
Grady's Avatar
Forum Topic Moderator
Join Date: Jan 2005
Location: Delaware, The First State
Posts: 13,936
Received 1 Vote on 1 Post
Low heat pressure switch?

Sorry, I've never heard of a low heat pressure switch. Do you have a wiring diagram you could copy & post?
 
  #3  
Old 11-20-08, 11:03 AM
Forum Topic Moderator
Join Date: Oct 2002
Location: Hamilton County, Ohio
Posts: 4,296
Received 2 Votes on 2 Posts
Look at your book again. I suspect it refers to the vent pressure switch. I can tell you that my son in law had this problem last week on a Goodman, and it turned out that the condensate drain line was plugged which caused the pressure change. Cleaning it and the trap cured his problem.

Also, look for a small vacuum line running from the inducer blower to the pressure switch. When the inducer is running, remove the line at the inducer fan and suck on it continuously. If the furnace then lites, the switch is okay and you need to do a cleaning as described above.
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
Display Modes
 
Ask a Question
Question Title:
Description:
Your question will be posted in: