Goodman 100-4

I have a Goodman 100-4. It has been messing up. It will kick on and go off after a few seconds after the flame has been lit. After some testing I thought it might have been the board. So I bought a white rodgers 50t35-743. After installing the board it would only get to heating up the HSI then shut completely off but keep the blower going when in auto fan. The 50T35-743 is suppose to be a replacement part for the B18099-13. I put in a new flame sensor and a new HSI. I also bypassed all that I could to rule out any other part. Now im just stuck. The transformer puts out 25v.

Please help
 
  #2  
Old 12-02-08, 06:29 PM
Grady's Avatar
Forum Topic Moderator
Join Date: Jan 2005
Location: Delaware, The First State
Posts: 12,682
Received 41 Upvotes on 39 Posts
White-Rodgers

I've heard of those boards but never used one. What are letters in front of the 100-4? Are you getting any kind of fault code? Pay particular attention to the instructions on page 3 of the installation sheet. http://www.white-rodgers.com/wrdhom/.../0037-6533.pdf
 
  #3  
Old 12-02-08, 06:36 PM
D
Member
Thread Starter
Join Date: Dec 2008
Location: missouri
Posts: 5
Upvotes: 0
Received 0 Upvotes on 0 Posts
sorry its a gmp. The only falut code that I get is 1 Blink which is an inigtion failure. But that is rare it just keeps trying to restart and that is on the old board the B18099-13. The new board just shuts it status light off.
 
  #4  
Old 12-02-08, 06:47 PM
Grady's Avatar
Forum Topic Moderator
Join Date: Jan 2005
Location: Delaware, The First State
Posts: 12,682
Received 41 Upvotes on 39 Posts
Gmp 100

Did you cut the white jumper wire between pins 4 & 7 on the 9 pin connector? If you have double & triple checked the installation, look at the "Diagnostic Features" on page 4 of the installation sheets.
 
  #5  
Old 12-02-08, 06:58 PM
D
Member
Thread Starter
Join Date: Dec 2008
Location: missouri
Posts: 5
Upvotes: 0
Received 0 Upvotes on 0 Posts
The old board is from the past owner. the 4 and 7 was already cut. on the new board I used the connector that was already there since it use to work great. When i use the 9 pin that came with the new board it just a power wires. I dont have an instaltion guide for the furnace. But will look for one again.
 
  #6  
Old 12-02-08, 07:04 PM
Grady's Avatar
Forum Topic Moderator
Join Date: Jan 2005
Location: Delaware, The First State
Posts: 12,682
Received 41 Upvotes on 39 Posts
Installation Guide

The installation guide I was refering to is the one for the White-Rodgers control. If you have misplaced it, I've provided a link in my first post.
 
  #7  
Old 12-02-08, 07:08 PM
D
Member
Thread Starter
Join Date: Dec 2008
Location: missouri
Posts: 5
Upvotes: 0
Received 0 Upvotes on 0 Posts
oh sorry. Ok im reading it right now it was only one sheet that they gave me. The only thing that i dont understand is when they say disconnect the edge card connector.
 
  #8  
Old 12-02-08, 07:34 PM
Grady's Avatar
Forum Topic Moderator
Join Date: Jan 2005
Location: Delaware, The First State
Posts: 12,682
Received 41 Upvotes on 39 Posts
Edge Card Connector

As I recall, the 13 board doesn't have an edge card connection but some of the earlier boards did.
 
  #9  
Old 12-02-08, 07:37 PM
D
Member
Thread Starter
Join Date: Dec 2008
Location: missouri
Posts: 5
Upvotes: 0
Received 0 Upvotes on 0 Posts
well there wasnt any other connections with the furnace. so im not sure if thats what its looking for
 
  #10  
Old 01-27-11, 07:52 PM
A
Member
Join Date: Jan 2011
Location: USA
Posts: 1
Upvotes: 0
Received 0 Upvotes on 0 Posts
Just ran up against this same problem

Hi all, yes I know this post is 2 years old but I wanted to share what I found on this same problem and how I handled it.

The B18099-13 PCB on my Goodman GMP has been acting up. I ordered a 50T35-743 and installed it this evening. The problems started when I tried to figure out where all the extra wires were supposed to go. Those wires were in my old 9 pin connector.

The Instructions for the B18099-13 expect that everyone has an edge connector on their furnace. My GMP was manufactured in March of 2001 and has no edge connector.

The 9 pin connector has the same connection points on the PCB as the edge connectors so all you have to do is move the pinned wires from the old 9 pin connector to the new 9 pin connector. For the GMP furnace the white wire that jumps between 1 and 4 is cut. I simply used a pin pusher and removed it alltogether.

The reason the gas valve never turns on is because all those permissives are not wired up.

Good luck!
 
 