honeywell smart valve troubleshooting

I have a rooftop HVAC unit with a smart valve SV 9500 M.
I have replaced that flame sensor - pilot assy with no results. When t'stat calls for heat, inducer motor starts and the pilot then lights. The main burrner does not come on. Am I right thinking the valve is the problem. If any safety device is open, the pilot would not light, isn't that right. I hate to just replace parts. Thanks
 
  #2  
Old 12-10-08, 06:30 PM
M
Member
Join Date: Dec 2004
Location: San Jose,Ca
Posts: 1,277
Upvotes: 0
Received 3 Upvotes on 3 Posts
Try wiggling the wires on top of the valve. The 9500 had an internal wiring problem. If it comes on by this method then you do need a new valve
 
 