Payne Plus 90 not lighting regularly 88,000 btu


  #1  
Old 12-13-08, 03:10 PM
M
Member
Thread Starter
Join Date: Dec 2008
Location: WI
Posts: 2
Upvotes: 0
Received 0 Upvotes on 0 Posts
Payne Plus 90 not lighting regularly 88,000 btu

I have an older Payne Plus 90 furnace that when we started using it this fall had water backing up in the exhaust fan area which started leaking and burned out our circuit board.

I have replaced the circuit board and opened the drain line but the hot ignite plate is not lighting all the time. For awhile if I taped on the little silver vacuum looking thing on the right side of the exhaust motor(I know I'm getting very technical here with all these big terms but just stay with me) the igniter would light.

Any help on what more I need to clean out? I blow though most of the drain lines and one did seem plugged that went into a black box type thing against the main part of the furnace that also has a line going to the silver vacuum thing but I was afraid to take that black box a part.

Does any one know what all has to be cleaned out or where there might be info about this?

Thanks
 
  #2  
Old 12-13-08, 05:10 PM
G
Member
Join Date: Oct 2002
Location: Hamilton County, Ohio
Posts: 3,927
Upvotes: 0
Received 2 Upvotes on 2 Posts
The silver thingy is the pressure switch. It checks for any venting obstructions, such as the water problem you describe. The condensate water should be going to a drain outside of the furnace. If the "black box has water lines into it and from it to the drain, it is a water trap. Clean out all lines and you should be back in business.
 
  #3  
Old 12-14-08, 10:30 PM
M
Member
Thread Starter
Join Date: Dec 2008
Location: WI
Posts: 2
Upvotes: 0
Received 0 Upvotes on 0 Posts
I took everything a part tonight. Cleaned all drain lines and put black stove sealant on all joints that I took a part to make sure everything was sealed.

Still won't light?
 
  #4  
Old 01-04-09, 08:25 PM
J
Member
Join Date: Jan 2009
Location: California
Posts: 3
Upvotes: 0
Received 0 Upvotes on 0 Posts
does your circuit board have LED?

Does your circuit board have an LED that blinks? My 90 plus is blinking 1 slow and 3 fast (13) which means that either their is a blockage, like filters cloged. or maybe the vacume switch is bad. (that round silvery thing) if not that maybe the pre ignition blower is bad. I am going to the appliance repair store to get a new , round silver thing tommorrow. The furnace guy said it would be $180 for them to put one in. I figure it shouldn't cost more than $40 at the store. (Hope I am right)

With only two screws and a couple of pull off low voltage plugs anyone should be able to replace it. '

In my case i am also having some water drip from a black plastic box by the burner chamber. do you know anything about that?
 
  #5  
Old 01-04-09, 09:21 PM
SeattlePioneer's Avatar
Banned. Rule And/Or Policy Violation
Join Date: Jul 2007
Location: Seattle, Wa
Posts: 4,469
Upvotes: 0
Received 1 Upvote on 1 Post
Originally Posted by jwolfenden
In my case i am also having some water drip from a black plastic box by the burner chamber. do you know anything about that?

I'd hold off replacing the pressure switch. With water still dripping from the furnace more than likely it's still flooded with water.

Frankly, it's confusing to try to sort out what's going on between two people having similar problems. Unless you choose to start a new thread and describe what's happening from scratch, I'll just let you sort things out between yourselves.

However, from the remarks that have been posted it sounds like both of you are mostly guessing and supposing about what's happening, which isn't generally a very good diagnostic method.
 
 