Carrier Gas Furnace Error Code

My churches Carrier Gas furnace (48GX-60115301) main board blinks 6 times suggesting my problem is a "blower motor fault". I can manually turn this on at the thermostat but the furnace will not start automatically nor heat in manual.
Does anyone have experience with this issue? I cannot find an owners manual nor a copy of the electrical schematic on the internet. Thanks for your help!! Steve:
 

Last edited by sking34; 02-22-09 at 03:01 PM. Reason: Liked the head banging better- just frustrated!
  #2  
Old 02-22-09, 05:14 PM
Grady's Avatar
Forum Topic Moderator
Join Date: Jan 2005
Location: Delaware, The First State
Posts: 12,682
Received 41 Upvotes on 39 Posts
Wiring Diagram

There is usually a wiring diagram on the inside of the blower door.
 
  #3  
Old 02-22-09, 05:45 PM
SeattlePioneer's Avatar
Banned. Rule And/Or Policy Violation
Join Date: Jul 2007
Location: Seattle, Wa
Posts: 4,469
Upvotes: 0
Received 1 Upvote on 1 Post
****Blink**** six times on the ceiling if you loooooove me---


twice on the pipes, if the answer is noooooooo----


My mind is a junk yard.


chorus
Oh my darlin
knock three times on the ceiling if you want me
twice on the pipe if the answer is no
oh my sweetness
means you'll meet me in the hallway
twice on the pipe means you ain't gonna show
 
  #4  
Old 02-23-09, 05:13 PM
E
Banned. Rule And/Or Policy Violation
Join Date: May 2007
Location: Wisconsin
Posts: 7,826
Upvotes: 0
Received 1 Upvote on 1 Post
I know the song.

To the poster,

I still think the furnace should start though. What probably happened is the blower did not work, so then the furnace high limited, and then you may have had to shut off and restart the furnace, to get it going again - and maybe you did not know that.

But you will still have to find out if the blower is seized up from bearings, bad motor windings, simply a bad capacitor, etc.

If you stop back, we can probably get quite speciific here in helping you out. For some reason though, I have this gut feeling that you have either solved it, perhaps with the assistance of various church know-it-alls, or got someone else to fix it since it was Sunday yesterday. Sunday...church.........
 
  #5  
Old 02-23-09, 05:26 PM
B
Banned. Rule And/Or Policy Violation
Join Date: Feb 2009
Location: Mi.
Posts: 11
Upvotes: 0
Received 0 Upvotes on 0 Posts
You probably have a bad circuit board.
There are seperate relay contacts for heating speed and A/C speed.
With the thermostat fan switch in the on mode the fan motor is energized in the A/C ( high ) speed.
With it in the auto setting then the furnace circuit board has control has control at a lower speed setting.
The relay is bad and that causes the relay to overheat and burn the solder off the back side of the circuit board.
DON'T resolder the board - replace it.
If you decide to resolder the board it will burn up the entire board and fill your house with smoke.
 
 