Coleman Furnace -Flame Goes Out!!!!
Old 03-02-09, 05:12 PM
Angry Coleman Furnace -Flame Goes Out!!!!
I have a Coleman Furnace (Model# 2960A656) with Flame Tube Style. The flame goes out (about once a week) and I have no heat. I have to reset the furnace in order to work properly.
Also Gas Valve setting is 2.6 inH20. I believe it should be 3.5 inH20 but everytime I adjust the valve the flame goes out. PLEASE HELP!!!!
Old 03-02-09, 05:47 PM
E
Received 1 Upvote on 1 Post
How do you know that is what that pressure reading is?
Have you been making adjustments with a pressure test device, like a manometer?
And HAD the unit been working good?, and then one day did not? Or was someone trying to 'fine tune' the gas valve to try to save gas, or?
Old 03-02-09, 06:04 PM
Yes, I have a manometer, I was told rule of thumb is 3.5 inH20. My gas valve seems to work fine at 2.6 inH20. However once a week the flame goes out but if I reset the furnace it seems to work fine again. Any suggestions!!!!!
Old 03-02-09, 06:24 PM
Grady's Avatar
Received 41 Upvotes on 39 Posts
Gas Pressure
The correct gas pressure should be on a label on the furnace.
Is the orifice the correct size as spec'd by the manufacturer?
"Flame Tube Style"??? Is this a single burner or multiple tubes?
Old 03-02-09, 06:46 PM
Furnace has a single burner. I changed the flame sensor and iginition module. The flame goes out once a week or even sometimes 4 times in 1 day. I have to reset the furnace in order to work porperly.
Old 03-02-09, 09:13 PM
No flame
Single burner? That furnace should have 3 burners. Anyway when it fails to light you should have a failure code telling you what safety tripped.
Old 03-03-09, 01:56 AM
My furnace does not have a "Failure Indicator" it was installed back in 1988 - it's pretty old !!!!
Old 03-03-09, 05:58 PM
E
When you say the flame goes out, be specific more in what happens exactly, and when.
And do you have direct spark igniton directly to the flame tube burner? (No HSI? No pilot?)
Old 03-03-09, 06:57 PM
T
Is this a mobile home furnace? If so, check your chimney. Holes in the flue will cause it to trip out. Take the cap off and look down the flue.