Tempstar 5000 Furnace Ingnitor problem
#1
Member
Thread Starter
Join Date: Mar 2009
Location: Colorado
Posts: 1
Received 0 Votes
on
0 Posts
Tempstar 5000 Furnace Ingnitor problem
The electronic ignitor is not lighting the gas heating element. This is an electronic pilot, not a gas pilot. How do I solve this problem?
#2
Ignitor
Somewhere between the ignition control & the ignitor the wires should plug together. Unplug them & use a voltmeter in the contol half of the plug to check for 120 volts during an ignition sequence. If you get 120 the ignitor is probably bad.
The only thing which can be done is replacing the ignitor.