Gibson Gas valve?
#1
Member
Thread Starter
Join Date: May 2009
Location: Southern NJ
Posts: 2
Upvotes: 0
Received 0 Upvotes
on
0 Posts

i have 3 yr old gibson(nordyne) GL1RA 090C 12B and i now have no heat. led flash 4, inducer runs, ignitor glows, then shuts down without a flame. 4 or 5 tries later shuts down flash4. i think the main board may be faulty, with the wires removed from the gas valve i get 11.4 volts across the bwn and yel wires. when the gas is demanded (after ignitor warm up) the voltage drops to 0 v. am i correct in thinking this two wire gas valve should have 24 volts when commanded open and 0 volts off?? with the valve plugged in i get .26 volts off and 0 volts when commanded across the two wires on the main board connector. anyone seen this? or have a recommended test for me to try?
gas valve coil resistance 2.04 M Ohms
i recently replaced the inducer vacuum switch, it was sticking and gave a a flash 3 about 2 months ago
gas valve coil resistance 2.04 M Ohms
i recently replaced the inducer vacuum switch, it was sticking and gave a a flash 3 about 2 months ago
Last edited by Chris Snyder; 05-19-09 at 07:29 PM. Reason: more information
#2
Member
Thread Starter
Join Date: May 2009
Location: Southern NJ
Posts: 2
Upvotes: 0
Received 0 Upvotes
on
0 Posts
ac-dc voltage
when i realized the voltage was ac not dc, i retested, during my tests the furnace fired and has been good ever since. hopefully its fine, but is anyone has seen this and recommends what to check next time, let me know
thanks
thanks