Pressure switch on Laars XL-3 Pool

Turned my Jandy oil fired Pool heater on, did not work. Checked power and had current to pressure switch. Bypassed pressure switch and heater fired up. What would cause pressure switch to malfunction and should I just replace pressure switch ($190.00) or are there other options?
 
  #2  
Old 08-14-09, 05:32 PM
Skip4661's Avatar
Member
Join Date: Dec 2008
Location: West Michigan
Posts: 255
Upvotes: 0
Received 0 Upvotes on 0 Posts
I glanced at the manual for your heater. The pressure switch reacts to water pressure. According to the manual your unit requires a minimum of 30 gallons per minute flow through the unit. Either you don't have enough water flow to pressurize the heater and close the switch or you have a defective switch. Make sure your pump and filter are ok.
 
 