Rheem Criterion II runs constantly, no heat

Hello,

We have a Rheem Criterion II furnace, model RGPH-10EAMR, dating from 1997, running on propane. Just recently it started running all the time, blowing unheated air (regardless of thermostat setting). Went through several troubleshooting steps, detailed below:

Shutting off power at the circuit breaker doesn't solve the problem; power back on = cool air blowing constantly.

The thermostat seems to work fine. It's a basic mercury unit, red and white wires. Open circuit resistance until heat is called for, then less than two ohms. Connections are good on the controller, and it didn't matter whether or not the thermostat was connected, nothing changed.

Plenty of propane in the tank, pipes all seem fine, no gas odor. (Although, even if there were no gas, it still shouldn't run all the time?)

The pressure proving diaphragm switch for the damper fan seems to work, or at least it clicks when mouth suction is applied. (Again, even if that didn't work, it shouldn't run all the time?)

Removed the cover for the controller. Upon holding in the safety switch for the outer panel, could see three LEDs, but couldn't read exactly what they are. They are vertically oriented. The bottom LED is amber, it illuminates briefly when the safety switch is pushed in, then goes dark. The top LED is green, seems to be a power on indicator, it lights steady green. The middle LED is also green. It also illuminates, but seems a little darker than the top one, maybe it is being pulsed on and off?

We had a new ignitor installed a few months back FWIW, but that seems very unrelated. The Rheem troubleshooting guide in the manual doesn't cover this problem.

Many thanks for any ideas!!
 
Sponsored Links
  #2  
Old 08-22-09, 01:42 PM
Banned. Rule And/Or Policy Violation
Join Date: May 2007
Location: Wisconsin
Posts: 8,629
Received 0 Votes on 0 Posts
Maybe a high-limit tripped out from the last time it ran. When that happens, the blower keeps running, only with loss of heat function. If ignition process even tries to occur, then this is not it.
 
  #3  
Old 08-22-09, 05:39 PM
Member
Join Date: Aug 2009
Location: Ontario Canada
Posts: 35
Received 0 Votes on 0 Posts
I would agree that it may be a limit has tripped for one reason or another. It is odd that it just started unless the unit had ran for some reason causing the limit to trip. There are 2 or 3 manually reset limits on your furnace, they are brown, round about the size of a nickel with a button on top, usually with a red spot on the button. There is 2 wires connected to them, one on each side. You can check these by pushing on the buttons to see if any of them click. You can hear the click when they reset. The are located on the burner tray, and on the combustion housing. Then restore power and see if that is the problem.

It that is not the problem, the only other solution would be some kind of power surge has shorted the intergrated fan control board. (circuit board).
 
  #4  
Old 08-24-09, 10:05 AM
Member
Thread Starter
Join Date: Aug 2009
Posts: 6
Received 0 Votes on 0 Posts
Thanks, will check limits

I saw the limits when poking around, but didn't know what they were. I'm away from the furnace for a couple of days, but will report back. *Very much* appreciated!
 
  #5  
Old 09-01-09, 07:18 PM
Member
Thread Starter
Join Date: Aug 2009
Posts: 6
Received 0 Votes on 0 Posts
Update on the high limits -- two of them *were* tripped, but unfortunately that didn't solve the problem. The furnace still blows cool air constantly when powered up, no matter what the thermostat setting is. Must be a problem in the controller ... $$. Thanks for the advice to check the limits, at least I know what those are now.
 
  #6  
Old 09-07-09, 02:04 PM
Member
Join Date: Sep 2009
Location: north carolina
Posts: 8
Received 0 Votes on 0 Posts
With regard to troubleshooting, if you can see the model and serial numbers, then you can google the model # which might be able to get a service manual on line to state what the problem is.
 
  #7  
Old 09-08-09, 10:18 AM
Member
Thread Starter
Join Date: Aug 2009
Posts: 6
Received 0 Votes on 0 Posts
Hi Paverette,

Good advice; we did have the service manual for this unit, and followed its troubleshooting flow chart. Unfortunately, many of the problems end up with the "fix" being to replace the controller board. We had this done just recently, and it did solve the problem, at considerable expense. Thanks to all for your advice, at least I am much more educated now.
 
  #8  
Old 04-17-10, 12:27 PM
Member
Join Date: Apr 2010
Location: USA
Posts: 1
Received 0 Votes on 0 Posts
Thanks..

I had this very problem in a condo I don't visit too often and mostly weekends. Hate calling the repairman on a Saturday and getting bent over. Opened up the unit, found 2 switches, one tripped. Reset it and it fired up like a champ.. It was right outside the burners, to the right.

Thanks!!!! Saved me a few bucks and time..
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
Display Modes
 
Ask a Question
Question Title:
Description:
Your question will be posted in: