Carrier Super Saver Gas Furnace Won't keep burning

My 23 yr old Carrier Super Saver Natural Gas Furnace model 58SSB060-CC starts burning but the flame goes out after a few seconds. I have replaced the Gas Control Valve and cleaned the Pilot orafice. What am I missing?
 

Last edited by billvista; 11-01-09 at 12:05 PM.
  #2  
Old 11-01-09, 11:52 AM
G
Member
Join Date: Oct 2002
Location: Hamilton County, Ohio
Posts: 4,295
Received 2 Votes on 2 Posts
Check for a flame sensor. The idea is to shut off the burners if no flame is detected so you don't fill the house with raw gas. Look for a metal rod which would be sticking up in the path of the flame from one of the burners. It will have a wire attached to the bottom. If you have this feature, remove it (usually only one or two screws). Clean it by wiping lengthwise with very fine steel wool, emery paper, or similar fine abrasive. You do not want to cut into the metal, just "shine" it up a bit. Then replace it and see if that cures your problem.
 
  #3  
Old 11-02-09, 03:37 PM
B
Member
Thread Starter
Join Date: Nov 2009
Location: new york
Posts: 5
Received 0 Votes on 0 Posts
Is this the Flame Senor???

Thanks GS. I looked and don't see anything that looks like a flame sensor going in near either of the three tubes whehe the flame shoots into. What I did find is two wires (one with a resistor in series) going to a sensor that is mounted through the box area just above the flame tubes i mentioned above. I removed this sensor and on the backside it has two extensions about 3" long that connect to the two ends of a 1/2" round device that's silver colored on one side and says "therm-o-disc" on the other side. Could this be the flame sensor? It looks to be in perfect condition and is not dirty at all. Of course, that doesn't mean it is working tho. Soi, how can I test it to make sure it is ok?
 
  #4  
Old 11-02-09, 04:35 PM
SeattlePioneer's Avatar
Banned. Rule And/Or Policy Violation
Join Date: Jul 2007
Location: Seattle, Wa
Posts: 5,499
Received 0 Votes on 0 Posts
The parts you pulled out are the flame rollout fusible link and the limit switch.


You have a Carrier three wire pilot ignition system.

You need to remove the pilot burner, remove the brass ferrule holding the pilot tubin in the pilot burner and remove and clean the pilot orifice that comes out. Also clean the pilot burner.

Reassemble and reinstall the pilot burner and the furnace will probably work OK.


Seattle Pioneer
 
  #5  
Old 11-02-09, 04:55 PM
GRIMKNOTME's Avatar
Member
Join Date: Nov 2009
Location: N.C. USA
Posts: 120
Received 0 Votes on 0 Posts
Originally Posted by billvista View Post
Thanks GS. I looked and don't see anything that looks like a flame sensor going in near either of the three tubes whehe the flame shoots into. What I did find is two wires (one with a resistor in series) going to a sensor that is mounted through the box area just above the flame tubes i mentioned above. I removed this sensor and on the backside it has two extensions about 3" long that connect to the two ends of a 1/2" round device that's silver colored on one side and says "therm-o-disc" on the other side. Could this be the flame sensor? It looks to be in perfect condition and is not dirty at all. Of course, that doesn't mean it is working tho. Soi, how can I test it to make sure it is ok?
Originally Posted by SeattlePioneer View Post
The parts you pulled out are the flame rollout fusible link and the limit switch.


You have a Carrier three wire pilot ignition system.

You need to remove the pilot burner, remove the brass ferrule holding the pilot tubin in the pilot burner and remove and clean the pilot orifice that comes out. Also clean the pilot burner.

Reassemble and reinstall the pilot burner and the furnace will probably work OK.


Seattle Pioneer

All sounds rite flame sensor will be in direst contact with flame and if flame on it will cut out ina few seconds but if cross-over bar is rusted flame will not go across all burners will not make it to flame sensor .. also could have a actual bug in orifice .........................
 
  #6  
Old 11-02-09, 05:29 PM
SeattlePioneer's Avatar
Banned. Rule And/Or Policy Violation
Join Date: Jul 2007
Location: Seattle, Wa
Posts: 5,499
Received 0 Votes on 0 Posts
There is no separate flame sensor. There is only the pilot burner.
 
  #7  
Old 11-02-09, 07:37 PM
B
Member
Thread Starter
Join Date: Nov 2009
Location: new york
Posts: 5
Received 0 Votes on 0 Posts
Thanks SeattlePioneer. I already did clean the Pilot Furrrule orifice, but still have the same problem. I'm not sure what else I should clean. Is the Pilot Burner the tube shaped part of the pilot burner assembly?
 
  #8  
Old 11-07-09, 09:48 AM
B
Member
Thread Starter
Join Date: Nov 2009
Location: new york
Posts: 5
Received 0 Votes on 0 Posts
Carrier Super Saver 58SSB060-CC Still Won't Stay Burning

I have replaced the Gas Valve and now the Pilot Burner assy but the burners will still not stay burning. The pilot and everything else looks good, but when the burners light, they go out in a couple of seconds. Most times all three burners don't even have time to light before the flame goes out. Im stumped, not to mention frustrated. My local carrier parts store guy said that there can't be much more wrong besides what I've replaced. He said that if the Limit switch that mounts in the heat chamber was bad, the blower would run all the time and the pilot wouldn't light. What's happening here is the opposite. The blower motor starts when the furnace cycles on, but then shuts down rather quickly, which i understand is normal, then the ignitor lights the pilot and then after about 5-10 seconds, the burner lights, then goes out. The Inducer motor seems to run fine. Any ideas beyond what has already been said earlier in this thread? Thanks.
 
  #9  
Old 11-07-09, 09:52 AM
SeattlePioneer's Avatar
Banned. Rule And/Or Policy Violation
Join Date: Jul 2007
Location: Seattle, Wa
Posts: 5,499
Received 0 Votes on 0 Posts
You need to do a better job of cleaning the pilot burner, or replace it.
 
  #10  
Old 11-07-09, 10:53 AM
B
Member
Thread Starter
Join Date: Nov 2009
Location: new york
Posts: 5
Received 0 Votes on 0 Posts
The Pilot Burner assembly is brand new. I just replaced it this morning and the furnace still acts the same way. The main burners won't stay burning. They go out after only a couple of seconds.
 
  #11  
Old 11-07-09, 11:21 AM
SeattlePioneer's Avatar
Banned. Rule And/Or Policy Violation
Join Date: Jul 2007
Location: Seattle, Wa
Posts: 5,499
Received 0 Votes on 0 Posts
You need to start over describing the sequence of operation in detail.

Turn the thermostat down until everything is off.

Then turn it up, noting each thing that happens. Don't miss anything. You would probably need to do this several times until you get all the detail down.


And measure the AC voltage across the gas valve contacts one and two, the main burner wiring. Do you have 24 VAC across those contacts when the main burner is on, and none when the burners are off?
 
  #12  
Old 11-07-09, 11:24 AM
SeattlePioneer's Avatar
Banned. Rule And/Or Policy Violation
Join Date: Jul 2007
Location: Seattle, Wa
Posts: 5,499
Received 0 Votes on 0 Posts
The circuit diagram for your furnace is at

http://www.xpedio.carrier.com/idc/gr...t/58ss-1si.pdf
 
  #13  
Old 11-07-09, 11:50 AM
SeattlePioneer's Avatar
Banned. Rule And/Or Policy Violation
Join Date: Jul 2007
Location: Seattle, Wa
Posts: 5,499
Received 0 Votes on 0 Posts
And describe the pilot flame, including it's color, size and position.


The pilot flame heats up a temperature sensitive electrical switch that turns on the main burner when it gets hot enough. If the pilot flame is marginal, it can turn the main burner on and off erratically as you appear to be describing.

Pretty much any other defect will cause the furnace to shut off the main burner and pilot burner and go through the ignition sequence again, beginning with lighting the pilot. You don't appear to be describing that process.

Possibly you don't have the gas valve adjusted to provide adequate gas pressure for the pilot burner, or you could have inadequate gas pressure to the furnace.
 
  #14  
Old 11-07-09, 03:26 PM
SeattlePioneer's Avatar
Banned. Rule And/Or Policy Violation
Join Date: Jul 2007
Location: Seattle, Wa
Posts: 5,499
Received 0 Votes on 0 Posts
Also possible---- using a propane pilot in natural gas equipment. This would produce an undersized flame.

Presumably the new pilot burner came with a new pilot orifice and the bag it came in is specified for natural gas.

A natural gas pilot orifice will typically fit the wire from a regular wire brush through the hole in the orifice. A propane orifice wont allow that wire to go through it.

If you have the orifice from the old pilot assembly, that might be worth checking.
 
  #15  
Old 11-09-09, 06:09 PM
E
Banned. Rule And/Or Policy Violation
Join Date: May 2007
Location: Wisconsin
Posts: 8,627
Received 0 Votes on 0 Posts
Just in the case you pop back in....does the inducer fan keep running, as it should, when the flame shuts off?

And have you checked the inducer to make sure the voltage coming out of it does not stop when the flame goes out? (The voltage should remain as long as the inducer stays going...and it should stay going also).

It is possible you have a bad connection at the control module -

-or a bad control module.

But checking the first 3 things is free. Shotgun replacing can get expensive.... and not very mentally rewarding, either.
 
  #16  
Old 12-01-09, 10:55 AM
C
Join Date: Nov 2009
Location: USA
Posts: 17
Received 0 Votes on 0 Posts
58SSB060-CC same problem

I have the same 58SSB060-CC model Carrier and the same problem: thermo calls for heat, ignitor lights the pilot, burner comes on, lights for approx :15 seconds and goes out - same repeats.

I have replaced the pilot tube assembly (3 wire, natural gas) and the elecrode (good spark); and have 24 VAC when the burner is on, none when burner is off.

Any help will be appreciated.
 
  #17  
Old 12-01-09, 11:41 AM
SeattlePioneer's Avatar
Banned. Rule And/Or Policy Violation
Join Date: Jul 2007
Location: Seattle, Wa
Posts: 5,499
Received 0 Votes on 0 Posts
Her Claude,


Please repost and start a new thread. It rapidly becomes confusing dealing with multiple problems in one thread.
 
 

Thread Tools
Search this Thread
 
Ask a Question
Question Title:
Description:
Your question will be posted in: