Gas Valve Honk when closing??


  #1  
Old 12-31-09, 11:24 AM
T
Member
Thread Starter
Join Date: Dec 2009
Location: Illinois
Posts: 1
Received 0 Votes on 0 Posts
Gas Valve Honk when closing??

I have a Carrier 58SX Weathermaker circa 1987. When the furnace starts it's cycle off, it makes a strange honking sound that's fairly loud right when the burner turns off. I cannot figure out what exactly is making the noise and how to quiet it.

I am guessing the valve is noisy because isn't the valve closing when it starts the cycle off process. It's not the inducer motor or blower motor. They both are running and continue to run when it makes this sound.

Any ideas?? Would the pressure switch make this sound?
 
  #2  
Old 12-31-09, 02:22 PM
SeattlePioneer's Avatar
Banned. Rule And/Or Policy Violation
Join Date: Jul 2007
Location: Seattle, Wa
Posts: 5,499
Received 1 Vote on 1 Post
Very likely it's the regulator in the gas valve that reduces gas pressure to that used by the burners.

I've seen that happen occasionally. I've never seen it cause any problems.
 
  #3  
Old 12-31-09, 08:00 PM
M
Member
Join Date: Dec 2004
Location: San Jose,Ca
Posts: 1,573
Received 3 Votes on 3 Posts
reg vent may be partially restricted
Is this a valve with 5 wires? If yes, look for the reg adjust screw cap, remove the cap and look for a very small hole in the side of the cap. That is the vent, and it may be plugged with debris. Clean and reinstall. DO NOT move the screw beneath the cap.
 
 