Honeywell ST9120C HEAT STAYS ON

The thermostat sends signal the Mini Zone control module in my closet and LED on the module indicates heat is off. The thermostat does not show flame indicator; however, the heat stays on. I think it might have something to do with the ST9120C board since the AC works fine and same thing happens on both thermostats. How and what should I test to see if a signal is going from the control board in closet to ST9120C to tell it to shut off. My thought is that something is staying energized thus not shutting off the heat.
 

Last edited by sthaas; 12-31-09 at 09:05 PM. Reason: update with additional information
Sponsored Links
  #2  
Old 01-01-10, 01:49 PM
Grady's Avatar
Forum Topic Moderator
Join Date: Jan 2005
Location: Delaware, The First State
Posts: 13,941
Received 5 Votes on 5 Posts
St9120

Disconnect the zone panel from the furnace. If the heat goes off, the problem is the zone panel.
 
  #3  
Old 01-02-10, 10:28 AM
Member
Thread Starter
Join Date: Dec 2009
Location: USA
Posts: 16
Received 0 Votes on 0 Posts
Looks like there is a small burn mark on the board near the emergency switch. The switch has been broken off. Not good to have clothes up near the board "love where the put it". Anyways, is there a way to bypass the board and wire one zone directly, so that I have heat. I was going to directly connect the thermostat to the wires going from the equipment terminal; however, not sure about the two wires from the zone damper. Any thoughts...
 
  #4  
Old 01-02-10, 11:34 AM
Grady's Avatar
Forum Topic Moderator
Join Date: Jan 2005
Location: Delaware, The First State
Posts: 13,941
Received 5 Votes on 5 Posts
Zone Dampers

I know you don't want to hear this but a zoned warm air system is generally a gross waste of money. That being what it is, let's see what we can do to get you heat.

If no zone is calling for heat, are the dampers open, closed, or some open while others are closed?
 
  #5  
Old 01-02-10, 04:33 PM
Member
Thread Starter
Join Date: Dec 2009
Location: USA
Posts: 16
Received 0 Votes on 0 Posts
Sorry, for the delay... I have no clue and not shure how to check. Was going to assume they all remain open and just direct wire the 4 from thermostat (zone 2) to equipment side. This zone os my upstairs my down stairs has gas fire place and never run heat in the down stairs so not worried about it.


Thank you so much... Again sorry for the delay had an appointment and going to do what I said within the hour.
 
  #6  
Old 01-02-10, 04:47 PM
Grady's Avatar
Forum Topic Moderator
Join Date: Jan 2005
Location: Delaware, The First State
Posts: 13,941
Received 5 Votes on 5 Posts
Maybe a bit of trial & error

No problem on the delay. Seems like a lot of folks are having heater trouble today (usually Saturdays are kind of slow).

I'll try to walk you thru this as best I can without knowing about the dampers but I need to know which wire goes to which terminal on the zone panel. Hopefully, the wires will be red, white, green, & yellow then go to terminals R, W, G, & Y.
 
  #7  
Old 01-02-10, 05:25 PM
Member
Thread Starter
Join Date: Dec 2009
Location: USA
Posts: 16
Received 0 Votes on 0 Posts
You are correct...
The zone also has a red and a white on m4 and m11 the damper...

On the same panel "equipment side" has just r, w, g, and y...
 
  #8  
Old 01-02-10, 05:31 PM
Grady's Avatar
Forum Topic Moderator
Join Date: Jan 2005
Location: Delaware, The First State
Posts: 13,941
Received 5 Votes on 5 Posts
Let's give it a try

Turn off the power to the zone panel & furnace.
Disconnect the stat wires from the panel & hook them to corresponding terminals on the "equipment side" or disconnect both sides & nut the wires together color for color. Let me know when done.
 
  #9  
Old 01-02-10, 05:38 PM
Member
Thread Starter
Join Date: Dec 2009
Location: USA
Posts: 16
Received 0 Votes on 0 Posts
done wired all 4 with wire nuts
 
  #10  
Old 01-02-10, 05:44 PM
Grady's Avatar
Forum Topic Moderator
Join Date: Jan 2005
Location: Delaware, The First State
Posts: 13,941
Received 5 Votes on 5 Posts
Time to test

Restore power to the furnace & panel.
Set the t-stat heat/cool to OFF.
Set t-stat fan switch to ON.
Give it a few seconds (maybe up to a minute) & see if the furnace fan is on AND blowing air thru the vents. If so, switch to HEAT & AUTO & turn the stat up. I'll be waiting.
 
  #11  
Old 01-02-10, 05:56 PM
Member
Thread Starter
Join Date: Dec 2009
Location: USA
Posts: 16
Received 0 Votes on 0 Posts
Restore power to the furnace & panel "DONE"
Set the t-stat heat/cool to OFF. "DONE"
Set t-stat fan switch to ON. "DONE"
Give it a few seconds (maybe up to a minute) & see if the furnace fan is on AND blowing air thru the vents. "DONE"

If so, switch to HEAT & AUTO & turn the stat up. I'll be waiting "I did and flame icon comes on the stat and unit comes on but no flame".
 
  #12  
Old 01-02-10, 05:59 PM
Grady's Avatar
Forum Topic Moderator
Join Date: Jan 2005
Location: Delaware, The First State
Posts: 13,941
Received 5 Votes on 5 Posts
No flame

So we've come 180, from too much heat to no heat?
 
  #13  
Old 01-02-10, 06:01 PM
Member
Thread Starter
Join Date: Dec 2009
Location: USA
Posts: 16
Received 0 Votes on 0 Posts
Yep...
Could having the other zone still connected cause an issue?
 
  #14  
Old 01-02-10, 06:04 PM
Grady's Avatar
Forum Topic Moderator
Join Date: Jan 2005
Location: Delaware, The First State
Posts: 13,941
Received 5 Votes on 5 Posts
Other Zone

Could be. Try disconnecting it. Just be careful not to short any wires to each other or anything metal.
 
  #15  
Old 01-02-10, 06:12 PM
Member
Thread Starter
Join Date: Dec 2009
Location: USA
Posts: 16
Received 0 Votes on 0 Posts
done with same results...
I know the unit is on but no flame and no air flow... But sounds like everything is running...
 
  #16  
Old 01-02-10, 06:16 PM
Member
Thread Starter
Join Date: Dec 2009
Location: USA
Posts: 16
Received 0 Votes on 0 Posts
take that back when the stat shows the flame icon and is set to auto the unit comes on "makes noise" but no flame and the fan is not running. Just tried the same heat but put fan to on vs. auto, get air but no heat "does not ignite" only thing connected to the board now it the 24v transformer and the zone 1 and zone 2 (damper wires red and white)
 
  #17  
Old 01-02-10, 06:18 PM
Grady's Avatar
Forum Topic Moderator
Join Date: Jan 2005
Location: Delaware, The First State
Posts: 13,941
Received 5 Votes on 5 Posts
Something else to try

Go to the furnace & turn off via the service switch. Leave off for 30 - 60 seconds then turn back on. Tell me what happens & when.
Note: Some furnaces upon restoration of power will bring on the fan & exhaust motors for up to a couple of minutes then start their ignition sequence.
 
  #18  
Old 01-02-10, 06:30 PM
Grady's Avatar
Forum Topic Moderator
Join Date: Jan 2005
Location: Delaware, The First State
Posts: 13,941
Received 5 Votes on 5 Posts
More furnace info

Make & model of furnace? Is there some sort of ignition control module & if so make & model, please. Does the model # of the gas valve start with SV?
 
  #19  
Old 01-02-10, 06:43 PM
Member
Thread Starter
Join Date: Dec 2009
Location: USA
Posts: 16
Received 0 Votes on 0 Posts
honeywell ignition 8601U
gas valve honeywell ? do not see model
tempstar see case model number exm36f19c1
 
  #20  
Old 01-02-10, 06:52 PM
Grady's Avatar
Forum Topic Moderator
Join Date: Jan 2005
Location: Delaware, The First State
Posts: 13,941
Received 5 Votes on 5 Posts
8601?

Couldn't find an 8601.
I presume that was a typo & was supposed to be S8610U?

When you break & restore power, what happens? Exhaust blower come on? Any attempt for ignition (sound of spark or pilot lights)?
 
  #21  
Old 01-02-10, 07:03 PM
Member
Thread Starter
Join Date: Dec 2009
Location: USA
Posts: 16
Received 0 Votes on 0 Posts
You are correct on the number...
I turned it off an noticed a small green light come on the ignition box. However went out touched the wire bundle and it came on and system ignited and we have heat. Loose wire in the unit, guess when opening the panels... Anyways will track this down... Tested to see if it would cut off and on like it is suppose too, and it does work quite nice

You said these zoned units are not the best configuration... What is my option with an upstairs and downstairs.
 
  #22  
Old 01-02-10, 07:10 PM
Grady's Avatar
Forum Topic Moderator
Join Date: Jan 2005
Location: Delaware, The First State
Posts: 13,941
Received 5 Votes on 5 Posts
Major $$$

Far & away the best option is a separate system for each floor. Since Tempstar won't let me into their tech section, is that furnace, by any chance, two stage? How about the A/C?
 
  #23  
Old 01-02-10, 07:17 PM
Member
Thread Starter
Join Date: Dec 2009
Location: USA
Posts: 16
Received 0 Votes on 0 Posts
Yes, two stage with AC... Live in Charleston SC, however, always had problems with the heat. Has a tech replace the ignition system last year and worked fine. Each January, brings new issues. I am going to just by another EMM3U and wire it back up. Cheaper then another system for the other zone.
 
  #24  
Old 01-02-10, 07:33 PM
Grady's Avatar
Forum Topic Moderator
Join Date: Jan 2005
Location: Delaware, The First State
Posts: 13,941
Received 5 Votes on 5 Posts
Two Stage

With only 4 wires from the stat, it means you only have a single stage stat & are not getting anywhere near the full benefit from a two stage furnace. Most 2 stage furnaces will go to high fire if the stat is not satisfied in 'x' minutes. Wiring to a 2 stage stat will hold the furnace in low unless the room temp is 2 - 3 degrees below the stat setting. The single stage stat & the furnace going into high fire could cause overheating problems within the furnace especially if only one zone is calling for heat. Time for me to hit the sack. I've been up since 4:15 this morning & have to get up tomorrow by 6:00. Glad things are working well now. Good night.
 
  #25  
Old 01-02-10, 08:20 PM
Member
Thread Starter
Join Date: Dec 2009
Location: USA
Posts: 16
Received 0 Votes on 0 Posts
Thank You! I hope you get a good nights sleep. You saved me from spending money on a tech. here is what I found the board EMM3U needs to be replaced. I also need to replace the wire harness on the ST910C. It "wire harness" has a white connector on either end, and the larger end plugs into the board. When i move it it cuts on and off the little green status light on the ignitor. If you could give me a link where I can purchase this I would appreciate this "just the wire harness". Thank you again...
 
  #26  
Old 01-03-10, 01:05 PM
Grady's Avatar
Forum Topic Moderator
Join Date: Jan 2005
Location: Delaware, The First State
Posts: 13,941
Received 5 Votes on 5 Posts
Wire harness

Slept like a log, thank you.
I doubt you can buy just the wiring harness but I'd bet the end of one wire is not fully seated in the molex connector. If you unplug the harness & while looking into it you can see one wire whose end is not the same length as the others, particularly if you tug gently on each wire. Radio Shack sells wire, the ends, & the tools you need to repair.
 
  #27  
Old 01-03-10, 08:27 PM
Member
Thread Starter
Join Date: Dec 2009
Location: USA
Posts: 16
Received 0 Votes on 0 Posts
Thank you again for the information and the help...
 
  #28  
Old 01-03-10, 09:21 PM
SeattlePioneer's Avatar
Banned. Rule And/Or Policy Violation
Join Date: Jul 2007
Location: Seattle, Wa
Posts: 5,503
Received 0 Votes on 0 Posts
Where is Ecman? Usually he is FIERCE on checking for poor electrical connections on plugs! He's really missed out on an opportunity to render some of his favorite advice!
 
  #29  
Old 05-02-10, 06:13 AM
Member
Thread Starter
Join Date: Dec 2009
Location: USA
Posts: 16
Received 0 Votes on 0 Posts
I replaced the old board with a HZ322 TrueZone zone control panel and been working great for months. Now I noticed one thing: in the past only one zone would cool or heat at a time. With this new panel it only closes the damper when only a single zone is calling. This was fine during the winter but noticed that my coils and the suction line were frozen 'yes blower working'. I am wondering since two zones are calling at the same time if this is the problem? Second is there a way to have it only cool a single zone at any given time? The unit is 10 years old and I have only cleaned the outside coils several times. Filters changed when they start to look dirty or when they say to be changed.
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
Display Modes
 
Ask a Question
Question Title:
Description:
Your question will be posted in: