True Blue

I have a tech 4 true blue 90 im not sure what the problem is but it has to do with pressure switch. when i turn on thermostat nothing happens but if i go and open heater pull the 1/4 hose off the the 2" pvc going outside and give the hose a little suction the fan comes on and after 30 seconds the furnace lights and works fine the other end of the 1/4 hose goes to the pressure switch. can anyone help me with this its a strait temp of -4 in north WI
 
Sponsored Links
  #2  
Old 01-02-10, 02:10 PM
Grady's Avatar
Forum Topic Moderator
Join Date: Jan 2005
Location: Delaware, The First State
Posts: 14,247
Received 23 Votes on 21 Posts
Pressure Switch

Check the exhaust & intake (if two pvc pipes outside) to make sure neither is blocked. Is there a steady plume of steam coming out of the exhaust while the furnace is running?
 
  #3  
Old 01-02-10, 06:19 PM
Skip4661's Avatar
Member
Join Date: Dec 2008
Location: West Michigan
Posts: 298
Received 0 Votes on 0 Posts
You may be getting water in that tube and it won't let that switch open after a heat cycle.
 