Olsen Duomatic Ultramax Gas Furnace (circa 1988) - upgrade fan/blower?


  #1  
Old 01-30-10, 08:23 PM
B
Member
Thread Starter
Join Date: Dec 2007
Location: Toronto, Canada
Posts: 2
Upvotes: 0
Received 0 Upvotes on 0 Posts
Olsen Duomatic Ultramax Gas Furnace (circa 1988) - upgrade fan/blower?

I have a Olsen Duomatic Ultramax Gas Furnace (circa 1988) - Can I upgrade the fan/blower to a larger unit? I'm finding that the heat/ac doesn't make it up to the second floor very well. I'm not sure if that's just a function of the furnace's age, number of registers on the second floor, both?

I thought if the blower was upgraded to something larger, the air would make it up to the second floor.

I've tried closing registers on the lower levels but I don't seem to get much air upstairs.

Any ideas?
 
  #2  
Old 01-30-10, 08:45 PM
SeattlePioneer's Avatar
Banned. Rule And/Or Policy Violation
Join Date: Jul 2007
Location: Seattle, Wa
Posts: 4,469
Upvotes: 0
Received 1 Upvote on 1 Post
The most likely problem is that the fan motor isn't set properly or the ductwork is improperly sized. You need a repairman who can analyzae the problem and determine the best way to solve it.

This would involve checking the BTU input of the furnace, the heat rise across the input and output of the furnace and the static pressure of the furnace. You need someone who can test those conditions and understand what they should be and how they relate to each other.

Probably not a DIY job. Indeed, you need to look for a highly competent repairman to analyze the problem, in my view.
 
  #3  
Old 01-31-10, 01:10 AM
F
Member
Join Date: Mar 2006
Location: Wet side of Washington state.
Posts: 16,321
Received 39 Upvotes on 31 Posts
I agree that it is more likely a duct design problem than anything. I also think that at 20+ years of age you should be thinking about replacing that furnace rather than dropping big bucks into modifying it.
 
 