Wiring a blower for a oil furnance


  #1  
Old 02-24-10, 08:00 PM
B
Member
Thread Starter
Join Date: Feb 2010
Posts: 1
Upvotes: 0
Received 0 Upvotes on 0 Posts
Wiring a blower for a oil furnance

I have a Miller--Lear Siegler Inc , Home Furnace Divison Holland Michigan--Model No MMMG-82-CoA Patent No 3223078 Serial No A208218. Can someone please tell me where I can find a wire diagram on how to wire the blower/fan?When I bought this furnace the blower was not wired to it.I have looked every where.Can someone PLEASE help me?Thanks!!
 
  #2  
Old 02-25-10, 01:57 PM
P
Temporarily Suspended
Join Date: Jul 2008
Location: NY
Posts: 10,265
Upvotes: 0
Received 0 Upvotes on 0 Posts
It seem that company was acquired by someone else. I can't seem to find the number nor the manual. If you can see what control board is in it, that might help.
 
  #3  
Old 02-25-10, 04:09 PM
E
Banned. Rule And/Or Policy Violation
Join Date: May 2007
Location: Wisconsin
Posts: 7,826
Upvotes: 0
Received 1 Upvote on 1 Post
....I think by Nordyne....................
 
  #4  
Old 02-25-10, 04:52 PM
Grady's Avatar
Forum Topic Moderator
Join Date: Jan 2005
Location: Delaware, The First State
Posts: 12,682
Received 41 Upvotes on 39 Posts
Miller MMG

You actually have an MMG that isn't rusted out or cracked? The last one I saw was close to 20 years ago.

If I remember correctly they have a Honeywell L4046 fan/limit. If so, one side of the fan motor should go to neutral & the other side to the "fan" terminal of the L4046.
 
 