Lennox furnace pilot trouble


  #1  
Old 11-30-00, 06:52 AM
mcoellner
Visiting Guest
Posts: n/a
Question

I have a natural gas Lennox furnace and the pilot light goes out.It may stay lit for hours, days,or weeks then go out.I have replaced the thermalcouple and adjusted the pilot flame.It is still doing the same thing.I am thinking the gas ignition valve is faulty.Any ideas?????Mick
 
  #2  
Old 11-30-00, 07:45 PM
Sharp Advice's Avatar
Admin Emeritus
Join Date: Feb 1998
Location: The Shake and Bake State USA
Posts: 9,927
Upvotes: 0
Received 6 Upvotes on 5 Posts
Lightbulb

Hi:mcoellner

Many thermocouples get replaced without any of us ever giving a thought to cleaning the connection in the mag head. So remove the new t-couple you installed and with a cotton swab wipe out the connection where the t-couple screws into.

Be sure the pilot flame isn't too large. It should just encompass <surround> the tip of the t-couple head. The t-couple should be glowing a cherry red hot color. If not, the pilot flame may be too large or too small.

Should this furnace be over 15 years old, I would suggest you have the local gas service utility company come and service and check it.

The furnace may have developed a hairline crack in the area of the pilot flame. When the firebox heats up the crack opens and the air from the fan might be blowing the pilot flame out.

Good Luck,
TomBartco
Natural Gas Energy Technician and Consultant.
Personal Quote:
"Drive Safely. The Life You Save, May Be Your Own."
 
  #3  
Old 12-01-00, 02:39 PM
fjrachel
Visiting Guest
Posts: n/a
Did you by any chance clean the pilot spud located in the pilot assembly. They have a tendency to build up a powder residue which will cut down on the pilot lite temperature. If your pilot lite seems lazy you can change termocouples from now till spring and it will constantly go out.
 
 