Goodman Furnace System Lockout

Ive go a newer Goddman furnace. My house is only 2 years old. Ive installed a Honewell HE260A humidifier on the return side. As long as I can remeber Ive been getting the system lockout (to many retrys). At first I just figured that I needed to change the filter. I have since gotten a 3M cleanable filter. Now just cleaning the filter doenst seem to work. Im not sure it doesnt have something to do with the humidifier. It comes on runs for like 10-15 mins then shuts off and I have to turn off the furnace and reset the breaker and it will run for another cycle. Right now Ive got the service panel off the furnace and the switch taped down and it seems to be running fine. So Im assuming that its getting starved of resh air to heat. Ive attached a few pics of my step up. Any advice would be great.



 
Sponsored Links
  #2  
Old 11-26-10, 03:05 PM
Grady's Avatar
Forum Topic Moderator
Join Date: Jan 2005
Location: Delaware, The First State
Posts: 13,928
Upvotes: 0
Received 0 Votes on 0 Posts
By "service panel" I presume you mean the panel to the blower cabinet.
If this is the case & the control board is also in that cabinet, I'm leaning toward a return air problem. Try taking out the air filter & putting the panel back on. If the problem goes away, so should that highly restrictive air filter.
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
Display Modes
 
Ask a Question
Question Title:
Description:
Your question will be posted in: