Lennox G40 no heat
Air inducer motor runs for maybe two seconds then stops. After 20 to 30 seconds furnace again tries to light but inducer motor will only run for two seconds. Any ideas?
#2
Generally speaking, the inducer motor should turn on and stay on as long as there is proper power supplied to the furnace and the thermostat is calling for heat.
Start by checking to verify that the thermostat is on. You can use a jumper wire between the R and W terminals on the furnace to bypass the thermostat. That ought to turn the furnace on and keep it on.
Start by checking to verify that the thermostat is on. You can use a jumper wire between the R and W terminals on the furnace to bypass the thermostat. That ought to turn the furnace on and keep it on.
#3
Member
Thread Starter
Join Date: Dec 2010
Location: Canada
Posts: 2
Upvotes: 0
Received 0 Upvotes
on
0 Posts
After extensive trouble shooting and having the luxury of a second furnace, I think I found the problem. The ignitor has a very high resistance compared to my other furnace ignitor. Somehow the circuit board must sense that the ignitor is serviceable. If it is not the inducer motor immediately shuts down.