Carrier furnace code 31

Carrier furnace will blow but no heat. no clicking of ignitor. have had high winds. Model 58MXA08-12.
 
Sponsored Links
  #2  
Old 02-19-11, 08:03 PM
SeattlePioneer's Avatar
Banned. Rule And/Or Policy Violation
Join Date: Jul 2007
Location: Seattle, Wa
Posts: 5,503
Received 0 Votes on 0 Posts
your furnace manual is at:

http://www.xpedio.carrier.com/idc/gr.../58mxa-9sm.pdf



The Carrier 3-1 diagnostic code usually indicates that the pressure switch on the furnace isn't closing.


That usually means you have a problem with the venting system of the furnace being impaired in some way.


I presume that when the thermostat calls for heat the inducer motor above the burners tunrs on and comes up to speed?
 
  #3  
Old 02-19-11, 09:26 PM
J
Member
Thread Starter
Join Date: Feb 2011
Location: USA
Posts: 4
Received 0 Votes on 0 Posts
yes that's what happens. Have furnace manual, wasn't sure if code 31 was due to pressure switch failure, or some kind of lockout due to high winds causing ventilation problems.
 
  #4  
Old 02-20-11, 01:36 AM
SeattlePioneer's Avatar
Banned. Rule And/Or Policy Violation
Join Date: Jul 2007
Location: Seattle, Wa
Posts: 5,503
Received 0 Votes on 0 Posts
5% of the time the problem is the pressure switch.

95% of the time the problem is someplace in the venting system.
 
  #5  
Old 02-20-11, 04:17 AM
J
Member
Thread Starter
Join Date: Feb 2011
Location: USA
Posts: 4
Received 0 Votes on 0 Posts
Any way to reset this? Have turned off power, hoping that would reset the switch. Is a pressure switch a do it myself thing? I know we have to get the part from Carrier.
 
  #6  
Old 02-20-11, 08:28 AM
SeattlePioneer's Avatar
Banned. Rule And/Or Policy Violation
Join Date: Jul 2007
Location: Seattle, Wa
Posts: 5,503
Received 0 Votes on 0 Posts
As I noted, it's VERY unlikely the thew pressure switch is the problem. Instead, it's very likely that there is a defect in the venting system of the furnace.

Is the inducer motor starting and coming up to speed when the thermostat calls for heat?

Is ice, snow or anything plugging the plastic vent pipe?

You can remove the pipe for incoming fresh air at the furnace and check to see if a leaf or other debris is impairing the air flow.

Check to see if water is trapped in a dip in the plastic vent pipe.

Check to be sure that the drain for the furnace is not plugged up and preventing water from draining out of the furnace.
 
  #7  
Old 02-20-11, 12:53 PM
J
Member
Thread Starter
Join Date: Feb 2011
Location: USA
Posts: 4
Received 0 Votes on 0 Posts
thanks we'll try looking checking the vents and water
 
Reply
Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
 
Ask a Question
Question Title:
Description:
Your question will be posted in: