it goes through all the cycles but the blower motor will not kick on any solutions
 

Last edited by hvactechfw; 05-02-11 at 06:13 PM. Reason: moved from another thread, please do not hijack threads.
  #2  
Old 05-03-11, 05:57 AM
Jay11J's Avatar
Member
Join Date: Sep 2001
Location: Rochester, Minnesota
Posts: 16,984
Upvotes: 0
Received 0 Upvotes on 0 Posts
Sounds like the motor or board may be an issue.

What happens when you set the t-sat fan switch to "ON"?
 
  #3  
Old 03-07-13, 10:32 AM
T
Member
Join Date: Mar 2013
Location: USA
Posts: 1
Upvotes: 0
Received 0 Upvotes on 0 Posts
I just had this happen to me. I took the circuit board out and quickly discovered the 120 volt input on the main relay to the fan was fried. I cleaned up the carbon from the arching and re-soldered it. The trace on the circuit board was burnt away a little but I was able to bridge it. The other option would have been to add a wire from the relay to the power input connection (labled L1). Hope this helps someone else.
 
 