fan only option

i have an upflow oil furnace.the wiring diagrams are shaky.does anyone know how to wire in the "fan only" option?
 
  #2  
Old 09-01-11, 08:42 AM
F
Member
Join Date: Mar 2006
Location: Wet side of Washington state.
Posts: 16,321
Received 39 Upvotes on 31 Posts
Generally on the thermostat connections you would connect R to G to run the blower constantly. You may not have a G terminal on an older furnace.
 
  #3  
Old 09-01-11, 04:54 PM
J
Member
Thread Starter
Join Date: Aug 2011
Location: usa
Posts: 7
Upvotes: 0
Received 0 Upvotes on 0 Posts
let me clarify;i have installed(and used on my old furnace) a timer to run the fan manually.i need to find what wire goes where on the furnace to rehook it.
thanx...joel
 
  #4  
Old 09-01-11, 05:00 PM
Houston204's Avatar
Forum Topic Moderator
Join Date: Oct 2009
Location: Texas
Posts: 6,532
Received 95 Upvotes on 88 Posts
Post the make and model of the furnace, make and model of timer. Pics might help.

As Furd has posted, R = 24VAC and G = fan.
Your timer will probably wire here but more information might carify this.
 
 